Results 1 to 3 of 3
  1. #1
    Join Date
    Apr 2009
    Location
    The Netherlands
    Posts
    16
    Rep Power
    0

    Maximum elevation alowed between compressor(cond)r and cooling coil (evap)?



    Gents,

    I have compressor and water cooled condenser mounted on a skid and air handling unit located above.
    What is the max. difference in bewteen?
    The cooling capacity is about 580kW.

    Thank you,
    rooibos



  2. #2
    Join Date
    Mar 2011
    Location
    Singapore
    Posts
    212
    Rep Power
    16

    Re: Maximum elevation alowed between compressor(cond)r and cooling coil (evap)?

    It's depend rooibos different manufacturers has different specifications.
    Also type of compressor is play a important role as well.
    Tell us more, what brand, or tailor made system, and model name and so on.
    580kW set is around 250Hp. How many compressor inside?
    Typical DX can go up to 30 meter is the most.

  3. #3
    Join Date
    Apr 2009
    Location
    The Netherlands
    Posts
    16
    Rep Power
    0

    Re: Maximum elevation alowed between compressor(cond)r and cooling coil (evap)?

    Thanks for your quick answer, Joe.
    At this stage of the project I don't have the brand. I was thinking for Bitzer's semi-hermetic compact screw compressors.
    So you think up 30 m is the most in general for DX?