20-04-2011, 03:22 AM #1
Re: Fridge Problem..frost on suction line, and cooling is not good
the condenser temperature from compressor to filter goes like this..
%55-60 is REALLY HOT to hot.. %15 warm.. %20-15 ambient.. while the suction line near the compressor is as cold as the evaporator.. maybe colder.
Yeah he did change filter, and installed a valve.
I wasn't around all the time after he finished welding.. but I recall him talking about using the manifold to measure pressure after vacuuming, and after charging.
I don't recall seeing a vacuum though.. what I understood from the portions I observed is that he welded everything and installed the valve.. then used the running compressor to vacuum itself.. but that is what I put together from what I saw.. is that even possible?
-
20-04-2011, 08:34 AM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Fridge Problem..frost on suction line, and cooling is not good
It looks like it is overcharged.
Did he weighed charge, charged from glass cylinder
or charged by monitoring only suction pressure?
Last is recipe for overcharging.Last edited by nike123; 20-04-2011 at 10:02 AM.