    Dear All,

    The duct shoes (square to round) emerging from the branches that will be connected to the flexible duct for subsequent connection to the diffusers,

    these shoes, when you connect them to the round volume damper, the entire piece (shoe plus damper), what length does it need to be as per smacna, is there a special formula for this?..

    Thank you,
    Regards



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: Duct shoes

    Dampers should generally be fitted at least 2 duct diameters downstream of any size change or direction change.