    mitsi heavy fault
    Hi guys,
    Can across the fault with HKXE2D R407c fault error E75.The manual stops till 45 ! The central remo con panl was all lit up and could not move any.Reset power and also of the outside units.All worked but after some time stopped again.
    Any idea ?
    Mar 2011
    Singapore
    212
    Re: mitsi heavy fault
    E75
    Central Controller communication error
    poor connection, broken wire, faulty controller
    Wiring between outdoor units' loop daisy chain and central controller are not clear.
    I highly suspected on poor connections... please check.
    Apr 2005
    Manchester England
    43
    332
    hi joe do you have a list of the codes as my list does not go past e50?
    Feb 2005
    sliema
    52
    138
    Found there were some units that were on cooling and others on heating.All worked fine till today from last week .
    Mar 2011
    Singapore
    212
    Quote Originally Posted by moondawn View Post
    Sorry moondown, I not very good in MHI products troubleshooting, but here is the link.
    http://www.mhiaa.com.au/docs/MHIAA_P...de_Book_A5.pdf
    I have some experiences on ME products.
    Hope that will help.
    Apr 2005
    Manchester England
    43
    332
    thanks joe that link is good