    Re: 4-stage cascade

    I've repaired few small leaks; repaired the second stage TXV and now trying to get it working properly with a mixture of R23 and R1150.

    Any idea on how much pressure is usually used by manufacturers in a TXV bulb?

  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: 4-stage cascade

    Quote Originally Posted by before View Post
    I've repaired few small leaks; repaired the second stage TXV and now trying to get it working properly with a mixture of R23 and R1150.

    Any idea on how much pressure is usually used by manufacturers in a TXV bulb?
    In the bulb is mostly the same refrigerant as the circuit it controls. The pressure is that pressure at the corresponding temperature.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Similar Threads

  1. r-23 low stage, cascade system
    By johnny1 in forum Refrigerants
    Replies: 8
    Last Post: 21-11-2009, 09:01 PM
  2. Building a 3 stage cascade
    By NoL in forum CPU Overclockers
    Replies: 9
    Last Post: 27-03-2009, 08:42 PM
  3. 3-stage cascade
    By before in forum CPU Overclockers
    Replies: 47
    Last Post: 22-02-2009, 11:18 AM
  4. Single stage Vs 2 stage comp rack
    By Kevin Yeo in forum Supermarket Refrigeration
    Replies: 0
    Last Post: 01-02-2007, 03:05 PM
  5. Regulation regarding hydrocarbons in an cascade
    By DaBit in forum Fundamentals
    Replies: 4
    Last Post: 19-01-2004, 12:42 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •