    Sep 2008
    new zealand
    problem for Mitsubishi compact ceiling cassette
    Hi I got a problem from my client, his heat pump is working for about 1 hour then stop, same thing happen several times each day, then he need to press the on button to start again. From the control PAR-JH240KA, I press the "check" button, the code P8 is come on, please anybody can help me for the above problem.
    Otto
    Mar 2011
    Dublin
    55
    14
    Re: problem for Mitsubishi compact ceiling cassette
    P8 is an outdoor fault code. It could be anything from a thermistor to a faulty contactor. It's not specific, problem is at your outdoor.
    Jun 2009
    Lusk , Dublin
    1,115
    Quote Originally Posted by eire1 View Post
    P8 tells you that you have a device active at the outdoor unit and the outdoor has registered the fault ,this does not necessarily mean the fault is with the outdoor unit !
    For example dirty filters can trigger a P8.
    Stu
    Sep 2008
    new zealand
    Hi all of the helper,
    I will try to have a look the outdoor unit, because this is a chinese restaurant, the outdoor unit just above the roof and may be just beside the kitchen exhaust fan. So if it is happen, can i just cleaning the thermistor or I need to replace it, and please kindly advice how to check the thermistor is working properly.
    Otto
    If it has them, check the LEDs of the outdoor unit, they will tell you more.
    Sep 2008
    new zealand
    Hi Brian,
    Thanks for your help, I will check the LED and let you know later.
    Otto