Hi I have a outdoor unit I put on test then the outdoor unit comes on the pipes starts freezing up and the receiver as well the outdoor fan just goes really slow for a min then it cuts out, put the gauges on when running on cooling gas pressure and power is fine on the indoor ducted unit theres no air pressure coming out of vents which it did work fine the code comes up on test run high abnormal temperature can any one help.
This unit is only 3 month oldLast edited by eurocooling; 17-02-2011 at 07:13 AM.
-
17-02-2011, 05:03 PM #2
Re: Mitsubishi electric PUH-P100
If you can provide exact model of the outdoor & indoor units together with the exact fault code that would be helpfull.
If the indoor unit does not run the fan or there is some reason why there is no air flow through the indoor coil then in cooling mode the suction will frost & the system will stop on a fault.
Perhaps something simple like closed fire damper in the ductwork ?
-
17-02-2011, 05:40 PM #3
Re: Mitsubishi electric PUH-P100
Sorry mate, we all have to get dirty sometimes.
Get in the ceiling.
Is the fan running?
If not - is there power to it, or a cap OK, or the windings normal resistance
If the fan is running - is the return duct clear, is the outlet ducting good.
With ducted a/c, you have to go into the ceiling, not troubleshoot from the outdoor unit, or the indoor outlets only.Last edited by paul_h; 17-02-2011 at 05:45 PM.
-
17-02-2011, 07:05 PM #4
Re: Mitsubishi electric PUH-P100
Hi indoor unit fan works fine the duct system all clean inside blows fine on fan only
-
17-02-2011, 07:18 PM #5
Re: Mitsubishi electric PUH-P100
Hi the code coming up on the remote after test run is U1 this says abnormal high pressure overheating safeguard operation the model is Mr slim Pead-100 hope you can help as I live in Portugal and mitsubishi are not the best help here
Regards
Jason
-
17-02-2011, 08:20 PM #6
Re: Mitsubishi electric PUH-P100
U1 is high pressure safety switch activation
On R410a thats 4.15 MPa or aprox 41 bar
Suggest look at the following items
1/ Indoor air flow in heating mode
2/ Outdoor fan in cooling mode
3/ Refrigerant flow blockage ( outdoor LEV locked shut )
4/ 4WRV not operating
-
17-02-2011, 08:23 PM #7
Re: Mitsubishi electric PUH-P100
service valves on the condenser closed,short of gas!
-
17-02-2011, 10:40 PM #8
Re: Mitsubishi electric PUH-P100
Or non-condensables.
The difference between genius and stupidity is that genius has its limits.
Marc
-
26-02-2011, 11:39 AM #9
Re: Mitsubishi electric PUH-P100
Hi again check everything on indoor unit blowing out hot air and cooling ok,when it gets to the vents nothing coming out this was perfect 3 months ago the outdoor unit comes on but the outdoor unit fan is very slow then compressor just switches of after 5 mins
-
26-02-2011, 12:23 PM #10
Re: Mitsubishi electric PUH-P100
Look for dampers in the ductwork, eg manual dampers used for balancing, electric dampers used for zoning or fire dampers designed to close with fusible links if commercial property.
Also butterfly dampers may be fitted in the outlets may have closed themselves.Last edited by paul_h; 26-02-2011 at 12:26 PM.
Similar Threads
-
mitsubishi electric v mitsubishi heavy ind
By coolhibby1875 in forum Air ConditioningReplies: 8Last Post: 04-09-2009, 01:42 PM -
Mitsubishi Electric P3 Error
By tonyh in forum Air ConditioningReplies: 2Last Post: 09-08-2009, 10:47 PM -
Mitsubishi Electric VRF
By vijay_study in forum Air ConditioningReplies: 3Last Post: 06-11-2008, 10:03 AM -
Mitsubishi Electric VRF help
By marc5180 in forum Air ConditioningReplies: 10Last Post: 04-11-2008, 09:40 AM -
mitsubishi electric a/c
By bellaman in forum Air ConditioningReplies: 6Last Post: 02-08-2008, 06:03 PM