26-02-2011, 10:32 AM #2
Re: Mc Quay MDS multi system
Try address the evap units 1,2,3,4,5 .
It's possible setting 0 is a default adress for a stand alone unit.If so the software may not search for multiple connected units.
S1 number 6 on the outdoor board should be on ,to tell the outdoor that there are 5 units connected.check page 99 &103 of attached doc.
http://www.uel.ru/downloads/IM-MDS%2...on%20Guide.pdf
Cheers