14-02-2011, 03:49 PM #1
Compressor goes off after few minutes
Hello everybody,
The compressor of a DX Unit (CLIMATECH) overflows and goes off after a few minutes of working and in the control panel there is an Alarm and shows error "HIGH SUCTION SUPER HEAT". I suspect this is due to the expansion valve (Not Sure). But the problem is, this particular valve is not available in UAE.
Model No. of Expansion Valve - ALCO K 0834 X 7428-2
Please some body help me to solve this issue.
Nidhin Cletus
-
14-02-2011, 04:03 PM #2
Re: Compressor goes off after few minutes
I think you mean OVERHEATS, not OVERFLOWS.
I think you are short on gas. Would you please check the subcooling?
-
15-02-2011, 06:45 AM #3
Re: Compressor goes off after few minutes
High - superheat can be due to 1) undercharged system 2) liquid line filter partially clogged 3) tex valve inlet port might have foreign particles
-
24-02-2011, 03:19 PM #4
Re: Compressor goes off after few minutes
Maybe you should post a bit more of information like what's the system for, refrigerant type, superheat, subcooling and any other visual and technical details you can provide. tho as D.D.KORANNE posted those are the high superheat related most common issues.
Similar Threads
-
Panasonic ducted just cuts out after a few minutes?
By paul_h in forum Air ConditioningReplies: 2Last Post: 17-11-2010, 09:09 AM -
degree minutes?
By dfaz in forum Air ConditioningReplies: 10Last Post: 10-10-2010, 08:53 PM -
I'm new to RE by a few minutes
By fanman in forum New to REReplies: 4Last Post: 09-08-2007, 04:27 AM -
Mitsubishi(s) Lock out in minutes
By fridge doctor in forum Air ConditioningReplies: 0Last Post: 19-06-2007, 09:22 AM -
Got 5 spare minutes ?
By WebRam in forum Computers & the InternetReplies: 0Last Post: 16-10-2004, 08:44 PM