09-01-2009, 05:26 PM #1
carrier 30GK 085
I have a problem with a carrier chiler model 30GK 085
this chiler can work with two set points i need to now how can i control it.
i now i have to conect or disconect two connections.
-
10-01-2009, 11:53 PM #2
Re: carrier 30GK 085
How are you controlling the chiller, local or remote control.
If you check the wiring to the following terminals this will help to tell you how this chiller is controlled remotely..
30 -31 remote alarm
32 -33 remote start stop
34 -35 remote water loop pump contacts or flow switch.
63 -64 remote cooling or heating
65 -66 remote cooling setpoint
Hope this helps
-
13-02-2011, 07:51 PM #3
Re: carrier 30GK 085
Does any of you know how to set the temperature down low than pre set +3.3*C. I have a customer with a 30GK 085 which would like to run it at -3*C. They have added glycol within the liquid mix.
I have contacted Carrier last week but are still awaiting there response. Do i need to change components to the unit for it to run sub zero?
-
13-02-2011, 10:14 PM #4
Re: carrier 30GK 085
According to the IOM for this unit to operate at -3C you will require some factory options either option 5 or 6 you will need to wait for Carrier to return your call to confirm which one you will need as for the glycol you have added you do realise you will reduce the capacity of the chiller, how much depends on the amount of glycol. Who did you call at Carrier ?
-
13-02-2011, 10:18 PM #5
Re: carrier 30GK 085
Do you have a controls manual?
http://eto.carrier.com/litterature/cm/13411.pdfBrian - Newton Abbot, Devon, UK
Retired March 2015
-
13-02-2011, 10:41 PM #6
Re: carrier 30GK 085
Forgot to add that Carrier Service would be needed as well to reconfigure the Service Configuration Software in the chiller control board.
-
14-02-2011, 09:02 PM #7
Re: carrier 30GK 085
Evening
Thanks for all the help.
We have the IOM and are aware the cooling capacity will be reduced depending on the glycol/temperature set. I spoke to Chris@ Carrier tech this morning and he cannot find any options that will alter the set points for the unit to run colder equired setpoint -3*c. He was going to speak to one of the Carrier engineers to see how to carryout the procedure. I'm still awaiting the call.
-
15-02-2011, 12:48 AM #8
Re: carrier 30GK 085
Option 5 (Medium Brine) allows leaving temperature from +5C to -6C at minimum requires reselected Electronic Valves and varnished compresser terminal plates.
Option 6 (Low Temp Brine) allows leaving temperature from -6C to -10C all of the above plus modified cooler and increased cooler insulation.
Also if the chiller is to be run at ambients below 0C then Option 28 is needed which is Condenser Varifans (variable speed fan motors) 1 per circuit.
As you can see its a bit more than just adjusting setpoints.
Similar Threads
-
MICROPROCESSOR DIAGNOSTICS/Differnces beteween TK/CTC
By REEFER-TEK in forum TransportReplies: 12Last Post: 27-03-2011, 04:12 AM -
30GK carrier chiller wiring diagram
By ash_sabi2006 in forum ElectricalReplies: 6Last Post: 20-05-2010, 04:26 PM -
Carrier Chillers
By Ed Burris in forum Technical DiscussionsReplies: 6Last Post: 27-03-2010, 02:00 AM -
Help identifying carrier HiWall dom. split
By paul_h in forum Air ConditioningReplies: 4Last Post: 12-12-2008, 09:12 AM -
carrier remote
By superswill in forum Trouble ShootingReplies: 2Last Post: 26-04-2006, 09:17 PM