28-08-2009, 02:14 PM #1
Cooling load for refrigerated warehouse
I'm sure this will seem like a very basic question but I'm trying to figure out how much energy it will take to cool a large storage and distribution warehouse.
There will be 7,500 m2 of freezer warehouse (-18 deg C) and 10,000 m2 of chilled warehouse (1 deg C).
Is there a benchmark of some sort as in W/m2 or kWh/m2/yr?
I'm currently working with a figure of 6.86 kW per 1,000 m2 for the freezer warehouse but I can't find anything for estimating the refrigerated warehouse.
Thanks.
-
14-09-2009, 06:51 AM #2
Re: Cooling load for refrigerated warehouse
you would need a whole lot more information than what you have provided to even give a guesstimate.
here are some points for you to consider:
type of insulation
thickness of insulation
ambient temperature
product being stored
temperature of product entering refrigerated space
storage
Pull down, if pull down time required to reach storage temp
volume of refrigerated space not m2
hopefully this will help you focus on what you need to determine.
Blythe
-
14-09-2009, 07:14 AM #3
Re: Cooling load for refrigerated warehouse
go to a warehouse and ask for the data, and learn learn learn.
asking here is bit too easy to get your paper.computer shooter
paul deelen
+31653300739
-
24-01-2011, 08:29 PM #4
New here...Where Should I Start?
hi i hope i enjoy my stay here pls be nice to me thanks!
-
10-02-2011, 07:48 PM #5
Re: Cooling load for refrigerated warehouse
~7kW per 1000m2 is 7W per m2. Calculation for the insulation thickness for the floor is 11W/m2...Don't count on that figure please
Be careful about reading health books. You may die of a misprint.
Similar Threads
-
Cooling Load Calculations
By hamidpia in forum Tools and CalculatorsReplies: 7Last Post: 05-02-2009, 08:57 PM -
Infiltration Cooling Load?
By Rankin755 in forum FundamentalsReplies: 4Last Post: 13-12-2008, 06:26 PM -
Heat transfer coefficient - Coolpack
By Graham in forum FundamentalsReplies: 10Last Post: 28-05-2008, 01:08 AM -
Compressor loading, cooling, and range of operation.
By Air duster in forum FundamentalsReplies: 10Last Post: 02-04-2008, 08:39 AM -
Cooling Load Calculation
By jervame_sireh in forum FundamentalsReplies: 0Last Post: 21-04-2007, 11:05 PM