02-02-2011, 07:14 AM #1
daikin split cycle airconditioner model rxd71Jvea
I have just been advised by a tech that the code presented on this unit has a code H27? in short the compressor is dead. He suggested I buy another split air conditioner as it wasn't worth repairing. Is the tech right with his diagnosis or can I replace the compressor. This unit is 10 years old and only used been usedon extreme temperature days . The compressor died on a day the temperature was 38-40 degrees celcius.
-
02-02-2011, 08:04 AM #2
Re: daikin split cycle airconditioner model rxd71Jvea
theres a few factors to consider here,
if the system is ten years+ parts may be difficult to source
what refrigerant the old system is, will it be replaced with a more energy efficient so running cost can be lower that can be offset against new install.g from R22 to R410A will be more energy efficient
is this the first of many problems to come
also if the system is in the UK there also UK F gas regs to take into account if the system is R22Paul
"KEEP IT COOL"
-
02-02-2011, 10:37 PM #3
Re: daikin split cycle airconditioner model rxd71Jvea
h27 isnt a daikin fault code.
check the compressor hasnt overheated and cut out on internal klixon
Last edited by Brian_UK; 02-02-2011 at 10:57 PM. Reason: didnt copy and paste properly
-
02-02-2011, 10:48 PM #4
Re: daikin split cycle airconditioner model rxd71Jvea
00OR ∗ Indoor unit in normal condition (Conduct a diagnosis of the outdoor unit.) —
A1Inverter unit - Faulty indoor unit PCB 89
A5Operation halt due to the freeze protection function or high pressure
control
90
A6Faulty fan motor (DC motor stop) DC motor 91
A6Faulty fan motor (AC motor stop) AC motor 93
C4Heat exchanger temperature thermistor or related abnormality 94
C9Suction air thermistor or related abnormality 94
CADischarge air thermistor or related abnormality 94
∗Faulty indoor unit PCB 95
96
∗OR U4 Faulty power supply or indoor unit PCB 97
U4Signal transmission error (between indoor and outdoor units) 98
UAFaulty indoor / outdoor power supply specification 99
∗OR E8 Operation halt due to detection of input overcurrent 106
E5Stoppage by OL actuation/Melt-down by temperature fuse 102
E6Opeartion halt due to compressor seizing 104
E7DC fan motor seizing 105
F3Abnormal discharge pipe temperature 101
H6Operation halt due to faulty position detection sensor 108
H8Operation halt due to detection of CT abnormality 109
H9Operation halt due to outside air thermistor abnormality 112
J3Operation halt due to discharge pipe thermistor abnormality, or due to
detection of disconnected discharge pipe thermistor
112
J6Operation halt due to outdoor unit heat exchanger thermistor abnormality 112
L5Operation halt due to detection of output overcurrent 110
U0Operation halt due to detection of insufficient gas 113
U2 Main circuit overvoltage or low voltage 115
-
02-02-2011, 11:23 PM #5
Re: daikin split cycle airconditioner model rxd71Jvea
H27 protective device for compressor is activated, compressor no. 2 oil sensor fault (disconnection,
sanyo???
-
02-02-2011, 11:25 PM #6
Re: daikin split cycle airconditioner model rxd71Jvea
H27 Off Off Off Off Outdoor Air Sensor Faulty Sensor Disconnected, Faulty or Contacts Dirty
panasonic?
-
03-02-2011, 10:32 AM #7
Re: daikin split cycle airconditioner model rxd71Jvea
Daikin fault codes are 2 characters, not 3, so it can't be H27, could be H7 for example.
The JVEA units aren't very good, parts are expensive, so I'd buy a new unit instead of repairing myself.
Similar Threads
-
MICROPROCESSOR DIAGNOSTICS/Differnces beteween TK/CTC
By REEFER-TEK in forum TransportReplies: 12Last Post: 27-03-2011, 04:12 AM -
Daikin Multi Split A/C problems
By timholmes204 in forum Air ConditioningReplies: 6Last Post: 22-05-2008, 12:09 AM -
Trouble with a daikin split, RXD71JVEA
By paul_h in forum Air ConditioningReplies: 12Last Post: 17-09-2007, 10:05 AM -
Daikin twin split
By Lippygit in forum Trouble ShootingReplies: 2Last Post: 28-07-2007, 06:28 PM -
Daikin Model
By Geofridgee in forum Air ConditioningReplies: 1Last Post: 12-07-2006, 09:23 AM