    daikin split cycle airconditioner model rxd71Jvea



    I have just been advised by a tech that the code presented on this unit has a code H27? in short the compressor is dead. He suggested I buy another split air conditioner as it wasn't worth repairing. Is the tech right with his diagnosis or can I replace the compressor. This unit is 10 years old and only used been usedon extreme temperature days . The compressor died on a day the temperature was 38-40 degrees celcius.



  2. #2
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    20

    Re: daikin split cycle airconditioner model rxd71Jvea

    theres a few factors to consider here,

    if the system is ten years+ parts may be difficult to source

    what refrigerant the old system is, will it be replaced with a more energy efficient so running cost can be lower that can be offset against new install.g from R22 to R410A will be more energy efficient

    is this the first of many problems to come

    also if the system is in the UK there also UK F gas regs to take into account if the system is R22
    Paul


    "KEEP IT COOL"

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: daikin split cycle airconditioner model rxd71Jvea


    h27 isnt a daikin fault code.
    check the compressor hasnt overheated and cut out on internal klixon
    Last edited by Brian_UK; 02-02-2011 at 10:57 PM. Reason: didnt copy and paste properly

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Talking Re: daikin split cycle airconditioner model rxd71Jvea

    00
    OR Indoor unit in normal condition (Conduct a diagnosis of the outdoor unit.) —

    A1
    Inverter unit - Faulty indoor unit PCB 89

    A5
    Operation halt due to the freeze protection function or high pressure
    control
    90

    A6
    Faulty fan motor (DC motor stop) DC motor 91

    A6
    Faulty fan motor (AC motor stop) AC motor 93

    C4
    Heat exchanger temperature thermistor or related abnormality 94

    C9
    Suction air thermistor or related abnormality 94

    CA
    Discharge air thermistor or related abnormality 94

    Faulty indoor unit PCB 95
    96

    OR U4 Faulty power supply or indoor unit PCB 97

    U4
    Signal transmission error (between indoor and outdoor units) 98

    UA
    Faulty indoor / outdoor power supply specification 99

    OR E8 Operation halt due to detection of input overcurrent 106

    E5
    Stoppage by OL actuation/Melt-down by temperature fuse 102

    E6
    Opeartion halt due to compressor seizing 104

    E7
    DC fan motor seizing 105

    F3
    Abnormal discharge pipe temperature 101

    H6
    Operation halt due to faulty position detection sensor 108

    H8
    Operation halt due to detection of CT abnormality 109

    H9
    Operation halt due to outside air thermistor abnormality 112

    J3
    Operation halt due to discharge pipe thermistor abnormality, or due to
    detection of disconnected discharge pipe thermistor
    112

    J6
    Operation halt due to outdoor unit heat exchanger thermistor abnormality 112

    L5
    Operation halt due to detection of output overcurrent 110

    U0
    Operation halt due to detection of insufficient gas 113

    U2 Main circuit overvoltage or low voltage 115

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: daikin split cycle airconditioner model rxd71Jvea


    H27
    �� �� �� protective device for compressor is activated, compressor no. 2 oil sensor fault (disconnection,
    sanyo???

  6. #6
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: daikin split cycle airconditioner model rxd71Jvea

    H27 Off Off Off Off Outdoor Air Sensor Faulty Sensor Disconnected, Faulty or Contacts Dirty
    panasonic?

  7. #7
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: daikin split cycle airconditioner model rxd71Jvea

    Daikin fault codes are 2 characters, not 3, so it can't be H27, could be H7 for example.
    The JVEA units aren't very good, parts are expensive, so I'd buy a new unit instead of repairing myself.

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Daikin Multi Split A/C problems
    By timholmes204 in forum Air Conditioning
    Replies: 6
    Last Post: 22-05-2008, 12:09 AM
  3. Trouble with a daikin split, RXD71JVEA
    By paul_h in forum Air Conditioning
    Replies: 12
    Last Post: 17-09-2007, 10:05 AM
  4. Daikin twin split
    By Lippygit in forum Trouble Shooting
    Replies: 2
    Last Post: 28-07-2007, 06:28 PM
  5. Daikin Model
    By Geofridgee in forum Air Conditioning
    Replies: 1
    Last Post: 12-07-2006, 09:23 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •