    70
    4,703
    47
    Airedale Ultima Chiller
    Has anyone any idea how to disable the Free cooling facility on the above chiller.
    We have had to isolate the free cooling water circuit through the condenser.
    Due to freeze damage of the pipework.
    However the valve and condenser fans are still operating as normal.
    Creating excessive sub cooling.
    I have tried disconnecting the ambient probe as suggested by Airedale.
    Which resulted in a probe failure alarm.
    Thanks Grizzly.
    Oct 2008
    mallorca, spain,
    75
    768
    Re: Airedale Ultima Chiller
    hi grizzly, yes I worked on a few of these < in the old days < normaly on free cooling the glycol is pumped from the dry cooler through the indoor unit < as you have seen< fi more cooling is requiered the 3way valves in the indoor unit change , the unit is in full cooling the glycol now goes through the small condencer taking the heat to the outside drycooler, the comps and all the 3way valves are in the indoor units< not much room < well thats the basics of thr system of corce this is 20 years ago and the set up may have changed, all the best = sedgy,
    just reread your post turn off the fans or turn off the glycol pumps
    3,853
    Could you warm the probe up so it thinks its too warm for free cooling? Or fit a resistor of the correct rating.
    There was a post about decade boxes the other day that would be a useful thing in this case.
    Down on the farm the correct way to get the condensing pressure up is with some fertilizer sacks....
    Jon
    70
    4,703
    47
    Not a stupid idea there Jon.
    Within the pco 3 software.
    There is a setting which looks for a minimum difference between the Sp and Ambient temperature.
    This was set at 2 degrees, Logic says change it to 20c and the freecooling will stop.
    No difference.
    Why I do not know?
    As previously mentioned Airedales advice was to disconnect the Ambient Probe.
    Whether I would of had more success linking out the probe connections, I don't know.
    5,667
    Not familiar with this model so I had a look on their web site.
    Even the Technical Manual doesn't give any clues. It's more like a Sales Brochure
    http://www.airedale.com/v2portal/pag...ontent_018.htm
    70
    4,703
    47
    I agree Frank.
    Hence the post, hoping someone in the know can help.
    Had a quick read of the install manual (doh), http://www.modine.com/web_server_con...C75-450_UK.pdf , and a couple of thoughts rose up slowly.
    As the free cooling is triggered when the outside sir is 1°C below the return water temperature would pulling the water sensor be a better bet than pulling the ambient? Clip the two together then they both read the same or if you disconnect the water sensor does it default to a -°C ?
    Secondly it seems that the favoured way of operation is the Variable Supply Temperature mode but the Constant Temperature mode seems to ignore water temperatures, or have I misread that?, might be something to try.
    Oct 2008
    mallorca, spain,
    75
    768
    hi grizzly, with all this confusion why dont you just go onto the controler and turn off the free cooling? entry code 1234, sedgy
    70
    4,703
    47
    Brian.
    I forgot to mention the chiller is required to be kept running, so if the return water temp probe is removed.
    We would loose control of the chilled water temp.
    You just may have something there?
    Sedgy.
    If I knew which setting to use I would.
    You are refring to accessing the Mk2 PCo by the way.
    Thanks guys for your input.
    Mar 2006
    Merate (LC) - Italy
    2,549
    IF it's an NTC, as per Carel standard, the higher the temperature, the lower the resistance. So, replace the NTC with a low value resistor until the free cooling no longer kicks in.
    70
    4,703
    47
    Quote Originally Posted by NoNickName View Post
    Good idea, well worth a try.
    Thank you.
    As I say I raised the ambient to SP minimum diff.
    But for some reason that did not work. If I am allowed to return to site.
    I will post how I get on.
  1. Replies: 12
  2. process chiller help
    By talon771 in forum Industrial
    Last Post: 12-01-2011, 08:42 PM
  3. Problems in r22 chiller design
    By umeshpradhan in forum Technical Discussions
    Last Post: 06-07-2010, 10:39 AM
  4. Airedale Chiller
    By pavilion in forum Air Conditioning
    Last Post: 22-01-2009, 08:22 AM
  5. Trane CVHE 450 R11 Centrifugal Chiller
    By albertjoseph in forum Air Conditioning
    Last Post: 06-10-2008, 03:23 PM