    cubecool's Avatar
    cubecool Guest
    Loss of Phase Current
    Hello, I have a Trane Chiller rtaa 216.
    It was running fine till about a 1/2 year ago.
    Now it's tripping on:Loss of Phase Current.
    I checked the compressorwindings with a ohmmeter,the current transformers and the cables.
    I also checked the contacters.
    Can anyone give a hint on what to do next?
    Apr 2001
    79
    5,071
    35
    Re: Loss of Phase Current
    Check and tighten wiring connections. A poor connection will overheat, so an IR thermometer can be very useful for this.
    70
    4,703
    47
    Hi Cubecool.
    Gary's advise is sound.
    What is happening is there is no current being sensed on one or more of the current transformer inputs.
    So I would check the obvious, if you have not already done so.
    That there is a phase supply to each of the run contactors.
    Just in case a line fuse has not blown?
    Secondly with the power off do you get continuity across the contactor terminals. Are there any signs of the overheating Gary mentions.
    Thirdly if voltages are OK then check out your CT coils.
    From what you describe something has failed, you just need to identify what.
    Good Luck Grizzly
    Oct 2010
    Greece
    52
    97
    14
    Hi Cubecool,
    Some units have double HP switches.
    Check external and internal reset of HP switch.
    You can also place a jumper (for test purpose) to HP switch to check if the compressor starts or not.
    You can also check or replace all auxiliary contacts of compressors contactors and you can check if the contactors coils are OK.
    If not, please let us know following:
    1. Is part winding or Y-D?
    2. If part winding has a 0,5 seconds timer or not?
    3. Year of manufacturing.
    Regards,
    CV
    Attached Files Attached Files
    cubecool's Avatar
    cubecool Guest
    Thanks guys,
    I checked the contacts of both the main contactors and
    replaced the starpoint contactor.
    I also checked the voltage to the contactors.
    Could there be something wrong in the controllboard?
    I wiil check your remarks as soon as I get to the chiller.
    Jan 2011
    sydney
    Only a stab in the dark, ( not familiar with model #)
    Is it a screw or a scroll? does it have a phase rotation /failure module? could there be a problem with that?
    Just thinking out loud.
    Mar 2006
    Merate (LC) - Italy
    2,549
    I think you could have a voltage unbalance that causes one phase to draw more current. Check and report back to us accordingly.
    Oct 2009
    merida mexico
    54
    282
    a very common problem on these machines is that the auxiliary contacts do not confirm the start of the compressor and this is read by the module and phase loss
    Apr 2009
    israel
    778
    Hi i have had to replace the control board ,it has the current inputs and might of blown a diode,
    i wouldnt change this board unless you narrow it down to that,check your ct's
    and check your inputs on the card.
    good luck
  1. Carrier Transicold Container Problem
    By Shamel in forum Transport
    Last Post: 23-01-2012, 11:23 PM
  2. Replies: 16
    Last Post: 08-12-2010, 07:56 AM
  3. SR2 50 models electric SBY diagonostics made simple
    By absolute-zero in forum Transport
    Last Post: 04-01-2008, 05:11 PM
  4. Replies: 5
    Last Post: 09-08-2007, 01:29 AM
  5. Phase Loss Detection
    By Latte in forum New Technologies
    Last Post: 03-01-2005, 10:01 PM
Tags for this Thread