Thread: Daikin U4 fault

  1. #1
    Join Date
    Sep 2010
    Location
    Seychelles
    Posts
    15
    Rep Power
    0

    Daikin U4 fault



    Hello all,

    I am fairly new here so please be gentle.

    Having a problem with some Daikin VRV machines we are installing in a hotel. We have had the systems (indoor and outdoor) running without incident for about two months now but we suddenly had a power failure on our site which cut off the main plant-room where most (but not all) of the outdoor units live.

    After the power came back all we see is the error code of 'u4' on all the remote controllers and none of the outdoor units will start up again.

    The system that did not get cut off by the power cut was fine and is still running without problems.

    We have tried shutting down all the units, all the remotes etc... to no avail, still get the U4 code and the machines will not run.

    We have also tried 're-setting' the pcboards by depressing the re-set button by nothing helps, still the same situation. The LED's on the PC board all light up, all the fuses are fine and there is good power getting to the units now....we just can't get the bloody things to start up again.

    Any help would be very much appreciated.

    Thanks,
    Seybrew



  2. #2
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: Daikin U4 fault

    u4 is a communication error to reset the outdoor board you need to press and hold reset on the master unit (led3 lit on outdoor pcb) whilst turning the power off then back on to the out door unit if this does not work then you need to check the supply and comms wiring it could well be the outdoor board that is faulty

  3. #3
    Join Date
    Sep 2010
    Location
    Seychelles
    Posts
    15
    Rep Power
    0

    Re: Daikin U4 fault

    thanks james, will try that tomorrow morning. We hit re-set but only tapped it as per the manual. I will hold it down and then re-set the power and see if that works.

  4. #4
    Join Date
    Feb 2009
    Location
    Australia
    Posts
    272
    Rep Power
    16

    Re: Daikin U4 fault

    SeyBrew,
    Had a u4 call today on a 5 year old Daikin wall split.
    Remote control was set on AUTO.
    Reset to Cool,,,,all good.
    Maybe it's that simple for you?i hope,
    easiest call i've done for a while,apart from the 2 snake in a damper motor duct last week.
    Lawrie
    Lawrie

  5. #5
    shimceltic's Avatar
    shimceltic Guest

    Re: Daikin U4 fault

    Quote Originally Posted by lawrence1 View Post
    SeyBrew,
    Had a u4 call today on a 5 year old Daikin wall split.
    Remote control was set on AUTO.
    Reset to Cool,,,,all good.
    Maybe it's that simple for you?i hope,
    easiest call i've done for a while,apart from the 2 snake in a damper motor duct last week.
    Lawrie
    Lawrie
    I had a u4 yesterday, had to dao a hard reset as mentioned here by holding reset and powering down outdoor and while still holding reset power back up. Then wait for h2p to stop flashing ( around 10 mins) once this has gone off or solid steart a new test so it can find all indoors.

  6. #6
    Join Date
    Sep 2010
    Location
    England
    Posts
    40
    Rep Power
    0

    Re: Daikin U4 fault

    You dont have to keep your finger on the reset button when powering down. If the isolator is further away than an arms length it is impossible.
    Power down then power back up and then put your finger on the reset button for 30secs, some people say 5secs and some people say 15secs.
    I find 30secs covers eveything

  7. #7
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: Daikin U4 fault

    Quote Originally Posted by wozza View Post
    You dont have to keep your finger on the reset button when powering down. If the isolator is further away than an arms length it is impossible.
    Power down then power back up and then put your finger on the reset button for 30secs, some people say 5secs and some people say 15secs.
    I find 30secs covers eveything
    Legally it should be possible as an isolator has to be within arms reach of the unit but i see your point it would be nice to live in a perfect world

  8. #8
    Join Date
    Sep 2010
    Location
    Seychelles
    Posts
    15
    Rep Power
    0

    Re: Daikin U4 fault

    Thanks for all the advice. We have managed to get the systems back up and running. Turns out it was a power issue. Some imbalance on the phases was causing the electronic protection to kick in and prevent start up. As soon as the power was sorted out, the units started up automatically.

  9. #9
    danair's Avatar
    danair Guest

    Re: Daikin U4 fault

    was the power fault detected at the outdoor unit or incoming power into the building? as i have a daikin reyq14 which i replaced a compressor on around a month ago which now has a u4 fault. thinking power problem could have bricked the old compressor. and is now interfering with indoors or buggard the pcb possibly?????

Similar Threads

  1. e4 fault code on daikin super inverter
    By Improver in forum Air Conditioning
    Replies: 13
    Last Post: 24-03-2011, 04:58 PM
  2. Daikin VRV U4 FAULT
    By leegally1983 in forum Air Conditioning
    Replies: 14
    Last Post: 30-11-2010, 11:49 PM
  3. Daikin r407c 2 pipe vrv ja fault code any offers?
    By Contactor in forum Air Conditioning
    Replies: 11
    Last Post: 28-07-2009, 01:26 AM
  4. Daikin Split f3 Fault
    By moondawn in forum Air Conditioning
    Replies: 18
    Last Post: 01-06-2009, 07:09 PM
  5. UA Daikin Fault Code
    By jedi in forum Air Conditioning
    Replies: 2
    Last Post: 23-07-2007, 01:44 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •