    Daiken Ac



    im new here and not an Expert of any sort Just a normal customer looking to install a heating Solution to thier new home.

    now my Question is i got an offer to install a VRV3 system by daiken. My main concern is comparing this to Inverter AC, in heating mode would i get cold air inside the house when the AC goes into Defrost cycle or not? and how Efficient the system would be?

    more over we don't have that cold winter in here it will be for about 20 days of the year with temps 0 Celsius would the system maintain the COP they had in the Brochure.

    Any thoughts are welcome and thanks



  2. #2
    Join Date
    Oct 2007
    Location
    United States
    Posts
    213
    Rep Power
    17

    Re: Daiken Ac

    Quote Originally Posted by Goodland View Post
    im new here and not an Expert of any sort Just a normal customer looking to install a heating Solution to thier new home.

    now my Question is i got an offer to install a VRV3 system by daiken. My main concern is comparing this to Inverter AC, in heating mode would i get cold air inside the house when the AC goes into Defrost cycle or not? and how Efficient the system would be?

    more over we don't have that cold winter in here it will be for about 20 days of the year with temps 0 Celsius would the system maintain the COP they had in the Brochure.

    Any thoughts are welcome and thanks

    Welcome Goodland,

    The Daikin system you are considering is one of the top of the line systems available world wide and is an inverter driven compressor system. As a heat pump it reverses the flow of the refrigerant in the winter to put heat into your home. If the installing company sizes it correctly it will produce all the heat you need and at even lower temps than you normally have.

  3. #3
    Join Date
    Dec 2010
    Location
    Palestine
    Age
    36
    Posts
    23
    Rep Power
    0

    Re: Daiken Ac

    Thanks mchild for your respond i will seek details of the offer and post them here to see if its correctly sized and what not i need to be doing my home work good because of the high cost of such system i dont want to be spend money and not getting to where i want !!

    anyway Thank you and happy new year

  4. #4
    Join Date
    Oct 2007
    Location
    United States
    Posts
    213
    Rep Power
    17

    Re: Daiken Ac

    Quote Originally Posted by Goodland View Post
    Thanks mchild for your respond i will seek details of the offer and post them here to see if its correctly sized and what not i need to be doing my home work good because of the high cost of such system i dont want to be spend money and not getting to where i want !!

    anyway Thank you and happy new year

    I failed to mention earlier that the indoor blower goes off during the defrost cycle so there is no cold air blowing. Good luck.

  5. #5
    Join Date
    Oct 2006
    Location
    UK
    Age
    57
    Posts
    165
    Rep Power
    18

    Re: Daiken Ac

    Hi,

    Just a point to remember, that on the VRV III heat recovery system the defrost control is very different compared to VRV II or any VRV system before that.
    On the VRV III each outdoor coil is defrosted one at a time. This means that you will not lose all heating capacity during the defrost cycle. Indoor units will continue to heat albeit at a reduced capacity. Much better that not having any heating while the system is busy defrosting.

    Best regards

    Obi Wan.

  6. #6
    Join Date
    Dec 2010
    Location
    Palestine
    Age
    36
    Posts
    23
    Rep Power
    0

    Re: Daiken Ac

    i will be having more details on everything hopefully by Monday but ideally the house in question is 200 m2 well insulated and double glassed, in tons or KW whats the capacity of the outdoor unit needed to have it running smoothly and efficient ?

  7. #7
    Join Date
    Dec 2010
    Location
    Palestine
    Age
    36
    Posts
    23
    Rep Power
    0

    Re: Daiken Ac

    :/ i cant edit my own posts !! anyway also i wont be using Heat Recovery VRV , the system i quoted is only capable of cooling or heating VRV III

  8. #8
    johno1953's Avatar
    johno1953 Guest

    Re: Daiken Ac

    hi guys im also new to game. im working on daikin vrv inverter,on full heating cycle,gauges are reading 14bar on suction and 8bar on discharge. the suction pipe is hot leaving the condensor but air coming out at fcu is cold any ideas. thanks john1953

  9. #9
    Join Date
    Sep 2010
    Location
    England
    Posts
    40
    Rep Power
    0

    Re: Daiken Ac

    Quote Originally Posted by johno1953 View Post
    hi guys im also new to game. im working on daikin vrv inverter,on full heating cycle,gauges are reading 14bar on suction and 8bar on discharge. the suction pipe is hot leaving the condensor but air coming out at fcu is cold any ideas. thanks john1953
    Is it a heat pump or heat recovery?

    What are the discharge and suction temperatures?

  10. #10
    Join Date
    Oct 2007
    Location
    United States
    Posts
    213
    Rep Power
    17

    Re: Daiken Ac

    Quote Originally Posted by Obi Wan View Post
    Hi,

    Just a point to remember, that on the VRV III heat recovery system the defrost control is very different compared to VRV II or any VRV system before that.
    On the VRV III each outdoor coil is defrosted one at a time. This means that you will not lose all heating capacity during the defrost cycle. Indoor units will continue to heat albeit at a reduced capacity. Much better that not having any heating while the system is busy defrosting.

    Best regards

    Obi Wan.
    Obi Wan,
    I assumed Goodland would be using a VRV-S model but thank you for that clarification.

    Glad to see you posting as it seems like it has been a long time since you were on this forum. You are always a world of knowledge.

  11. #11
    Join Date
    Oct 2006
    Location
    UK
    Age
    57
    Posts
    165
    Rep Power
    18

    Re: Daiken Ac

    Hi MChild,

    Good to hear from you, How is life in the USA...Is your VRV Mini still working at its best?

    Best Wishes

    Obi Wan.

  12. #12
    Join Date
    Oct 2007
    Location
    United States
    Posts
    213
    Rep Power
    17

    Re: Daiken Ac

    Quote Originally Posted by Obi Wan View Post
    Hi MChild,

    Good to hear from you, How is life in the USA...Is your VRV Mini still working at its best?

    Best Wishes

    Obi Wan.

    Obi Wan,

    You have a PM.

  13. #13
    Join Date
    Dec 2010
    Location
    Palestine
    Age
    36
    Posts
    23
    Rep Power
    0

    Re: Daiken Ac

    okay so the Contractor suggested that we need 14 Hp model Number RXYQ14PA, on 6 indoors units, the space its gona be heated/cooled is about 200m2 is this pump good enough for cold days when External temps is about 0c ?

    and also when it do defrost, as this is a single outdoor unit, what happens to the internal one would they blow cold air or just shut ?

    Thanks

  14. #14
    Join Date
    Oct 2006
    Location
    UK
    Age
    57
    Posts
    165
    Rep Power
    18

    Re: Daiken Ac

    Quote Originally Posted by Goodland View Post
    okay so the Contractor suggested that we need 14 Hp model Number RXYQ14PA, on 6 indoors units, the space its gona be heated/cooled is about 200m2 is this pump good enough for cold days when External temps is about 0c ?

    and also when it do defrost, as this is a single outdoor unit, what happens to the internal one would they blow cold air or just shut ?

    Thanks
    Can you give us the model number of the indoor units?

  15. #15
    Join Date
    Dec 2010
    Location
    Palestine
    Age
    36
    Posts
    23
    Rep Power
    0

    Re: Daiken Ac

    Indoor Units :
    1- FXFQ125P9
    2- FXFQ40p9 <<< 3 of those
    3- FXFQ50P9
    4-FXSQ125P

  16. #16
    Join Date
    Oct 2006
    Location
    UK
    Age
    57
    Posts
    165
    Rep Power
    18

    Re: Daiken Ac

    Quote Originally Posted by Goodland View Post
    Indoor Units :
    1- FXFQ125P9
    2- FXFQ40p9 <<< 3 of those
    3- FXFQ50P9
    4-FXSQ125P
    Ok so lets work this out.

    Indoor units Index
    FXFQ125P9 125
    FXFQ40P9 40
    FXFQ40P9 40
    FXFQ40P9 40
    FXFQ50P9 50
    FXSQ125P 125

    Total index 420

    Outdoor unit
    RXYQ14P maximum index @ 130% = 455

    455/1.3 = index @ 100% = 350

    420/350 = 1.2 x 100 = actual connected index of 120%

    Now look in the data book under heating capacity for RXYQ14P with;
    ambient temp at 0°C
    indoor temp at say 16°C
    with a connection ratio of 120%
    (see attached)

    It gives you total heating capacity of 40.4kW or 40400 watts

    Now 404000 / 200 m² Floor space = 202 watts per 1m² assuming everything is working flat out.

    More than enough I think. But if you don’t install remote room sensors for each indoor unit you may need a thick coat….

    Regards

    Obi Wan
    Attached Images Attached Images

  17. #17
    Join Date
    Dec 2010
    Location
    Palestine
    Age
    36
    Posts
    23
    Rep Power
    0

    Re: Daiken Ac

    Quote Originally Posted by Obi Wan View Post

    More than enough I think. But if you don’t install remote room sensors for each indoor unit you may need a thick coat….

    Regards

    Obi Wan
    LOL mate

    the senors are BRC1D52

    and got couple of Questions...

    so if the outdoor unit Goes into defrost the indoor units will blow cold air or will just stop, in other words how it will do defrost ??? using Aux heaters or just revers cycle

    and if we used 2 small outdoor units would it be more efficient on the electricity bill.

    and as this is going to be used for home is it better to use outdoor air to keep the air quality good or no ?

    Thanks mate you are officially my hero atm

  18. #18
    Join Date
    Oct 2006
    Location
    UK
    Age
    57
    Posts
    165
    Rep Power
    18

    Re: Daiken Ac

    so if the outdoor unit Goes into defrost the indoor units will blow cold air or will just stop, in other words how it will do defrost ??? using Aux heaters or just revers cycle

    When the outdoor unit perform the defrost cycle, the fans will automatically stop on the indoor units. The defrost function will switch the outdoor heat exchanger from evaporator to condenser automatically and then back again when compete. See the attached.

    and if we used 2 small outdoor units would it be more efficient on the electricity bill.

    The RXYQ12P has 1 x inverter compressor (speeds up and down as load is required) and 1 x direct-on-line compressor (is either on or off)

    To replace with 2 smaller outdoor units you will need to have
    RXYQ5P (1 x inverter compressor)
    RXYQ8P (1 x inverter compressor)

    RXYQ12P has a COP of 3.97 (coefficient of power)
    RXYQ5P has a COP of 4.00
    RXYQ8P has a COP of 4.50

    So yes two systems, would be more energy efficient than one. But the cost to install will be higher. The added bonus of installing two systems is in case there is a problem say with the outdoor unit, you will not lose all heating capacity, which may be important for residential application.

    and as this is going to be used for home is it better to use outdoor air to keep the air quality good or no ?

    I assume you are talking about ventilation. I would recommend that you investigate the Daikin VKM—GV1 heat reclaim ventilation unit. This will provide fresh air and extract air, but will also recover heat from extract air to fresh air. In addition you can also connect it to the VRV system to further heat or cool the supply air. It has an integrated XD coil and controls.

    Hope that helps.

    Obi Wan
    Attached Images Attached Images

Similar Threads

  1. DAIKEN FTXD71JUEA is it the compressor???
    By TECH TIM in forum Air Conditioning
    Replies: 2
    Last Post: 18-05-2010, 11:07 AM
  2. Daiken out door unit
    By kuti in forum Air Conditioning
    Replies: 1
    Last Post: 02-04-2010, 11:23 PM
  3. Daiken VRV II HELP!
    By jbomba in forum Trouble Shooting
    Replies: 4
    Last Post: 11-02-2010, 08:21 PM
  4. Daiken FLX60JVEA tries to start but cuts out
    By PADDYC in forum Trouble Shooting
    Replies: 9
    Last Post: 20-10-2009, 09:21 AM
  5. Absolute Zero, Daiken manuals
    By deu58 in forum Transport
    Replies: 3
    Last Post: 19-05-2008, 12:59 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •