30-11-2010, 01:14 AM #1
Help on a Shinco KFR-50GW/BMVE 18000 btu mini split heat pump
Short story: I did the majority of the install myself by running the electrical, setting the evaporator and condensing units, running the linesets. I was as careful as possible.
I left the following for my tech:
- Tighten flare nuts on linesets
- Evacuate the system
- Release *****
- Check for leaks
The interior unit runs and condensor fan kicks on for about 10 second bursts, but the compressor never fires.
Do these units have a pressure sensor? I'm wondering if maybe a pressure sensor is faulty?
Planning on calling Shinco tomorrow.
-
30-11-2010, 08:04 PM #2
Re: Help on a Shinco KFR-50GW/BMVE 18000 btu mini split heat pump
225psi at 73°F only proves the type of refrigerant in the system not the quantity.
What does the F0 code mean?
edit:
Just checked the forum for previous Shinco problems, read this thread...
http://www.refrigeration-engineer.co...ad.php?t=22466
There is a fault code list, some wiring problems resolved and also the code F0 which means a refrigerant shortage.Last edited by Brian_UK; 30-11-2010 at 08:13 PM. Reason: Added link
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
01-12-2010, 12:26 AM #3
Re: Help on a Shinco KFR-50GW/BMVE 18000 btu mini split heat pump
Thanks Brian,
I was able to download the fault code list, but "FO" isn't listed. My tech will try Shinco again tomorrow.
-
01-12-2010, 02:03 PM #4
Re: Help on a Shinco KFR-50GW/BMVE 18000 btu mini split heat pump
If the "FO" code does mean low *****, but there is some level of ***** in the system (seems to be at the same pressure as when installed and the factory charge should work with my ~12 foot lineset), then I'm wondering if maybe I've got a faulty pressure sensor?
There appears to be a pressure sensor on the condensor coil (see attached diagram, part number 10).
Would it do any harm to warm that sensor up with an electric heat gun? My thinking is maybe that's a thermal switch. Am I all wet here?
Thanks.
-
01-12-2010, 05:36 PM #5
Re: Help on a Shinco KFR-50GW/BMVE 18000 btu mini split heat pump
Sorry to keep posting on my own thread, but this may help others.
I spoke to Mike this morning at GT-World (Shinco) and he indicated that code "FO" meant a bad control board. Mike was very helpful and is sending out a new control board that my tech will install.
I'm wondering if the code "PO" that they show in the codes manual was supposed to be "FO" but got mixed up in translation -- seems plausible.
I'll post up once I get the control board and install it.
Thanks.
-
03-12-2010, 09:25 PM #6
Re: Help on a Shinco KFR-50GW/BMVE 18000 btu mini split heat pump
Good i hope that fixes the problem cross your fingers because im still waiting on a fan moter sence aug 2010 for the 50gw/bmve
-
04-01-2011, 12:37 AM #7
Re: Help on a Shinco KFR-50GW/BMVE 18000 btu mini split heat pump
Wanted to close out this thread.
The replacement circuit board arrived and did fix the "FO" code my unit was showing. Unit seems to work fine now.
Similar Threads
-
Design heat pump for a pool
By rolandh in forum Heat PumpsReplies: 10Last Post: 23-09-2010, 10:50 AM -
DIY heat pump 12kW
By kimusabi in forum FundamentalsReplies: 11Last Post: 17-10-2009, 07:50 PM -
Homemade Heat Pump...
By AC_Hacker in forum New to REReplies: 0Last Post: 29-04-2009, 11:30 PM -
Pool heat pump water side diagram
By nike123 in forum Heat PumpsReplies: 23Last Post: 22-03-2009, 07:42 PM -
Will this heat pump work?
By goodguy in forum Heat PumpsReplies: 7Last Post: 08-03-2008, 04:14 PM