    Re: Speed in evaporator tube

    Q=m'*dH - capacity [kW]
    m' - mass flowrate [kg/s]
    dH - difference of enthalpies of evaporating and suction refrigerant [kJ/kg]
    Acording to this formula you can calculate m'. After with help DesA's formula you can calculate velocity. Entalpy you can find using CoolPack.

    dP=lamda*(l/d)*(r*v^2)/2 - pressure drop on straight tube [Pa]
    lamda - friction coefficient, for copper tubes lamda=0.03
    l - tube's length [m]
    d - inner diameter of tube [m]
    r - density (vapour, or liquid, or 2-phase) [kg/m3]
    v - velocity [m/s]

    P.S. for more accuracy for 10^5< Re < 10^8
    lamda=0.0032+(0.221/(Re^0.237))
    Re - Reynolds number
    Last edited by Aik; 31-12-2010 at 09:40 AM. Reason: correction spelling errors
    In some places will have to think ...

Similar Threads

  1. Low speed Variable Speed Screw Chiller
    By MelbourneEngg in forum Technical Speculations
    Replies: 4
    Last Post: 02-07-2010, 02:33 PM
  2. Setting Daikin VRV indoor unit fan speed
    By mchild in forum Air Conditioning
    Replies: 8
    Last Post: 24-10-2009, 07:34 AM
  3. LG heat pump problem
    By back2space in forum Heat Pumps
    Replies: 132
    Last Post: 01-02-2009, 11:23 PM
  4. Speed control of the compressor
    By Peter_1 in forum Air Conditioning
    Replies: 10
    Last Post: 19-12-2007, 07:51 AM
  5. Thermo King OptiSet
    By REEFER-TEK in forum Transport
    Replies: 4
    Last Post: 06-12-2007, 07:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •