charging a 410 split system,can you charge in 60degree weather
I was trying to install my first r410a split system. I was told you can only charge with liquid, does this mean when bottle is upright it is in liquid position unlike r22 you turn upside down.Also can you properly charge a unit with an ambient temp of 58 Fahrenheit.I got a 200 psi both high and low side.Theirs a metering valve in the evaporator,could this be in backwards? Do I have a big problem? Started with 300 micron 12 hr.vacume.Then started to charge.I'm good with r 22 so what do i need
-
15-12-2010, 07:58 PM #2
Re: charging a 410 split system,can you charge in 60degree weather
Yes, only charge liquid.
Most bottles should have a dip tube and this should be stated on the bottle. If it has then do not invert it; if it hasn't then turn it over.
You should be charging by weight.
You say you have 200psi on both sides, is that standing pressure or with the unit running?
You can charge at almost any temperature if you have the right equipment.
Are you charging the whole system or just the lineset quantity?Brian - Newton Abbot, Devon, UK
Retired March 2015
-
15-12-2010, 09:00 PM #3
Re: charging a 410 split system,can you charge in 60degree weather
Hi Brian UK, I always thought it was bettter to charge systems on a hot day. What equipment is necessary to charge in any temperature?
-
15-12-2010, 10:06 PM #4
Re: charging a 410 split system,can you charge in 60degree weather
A bottle warmer perhaps.
Some systems have charging tables which give required superheat/subcooling against ambient temperature I believe, so sometimes you may be outside of the tables range.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
15-12-2010, 10:42 PM #5
Re: charging a 410 split system,can you charge in 60degree weather
I carry an internal source of a warm fluid, on a cold day I release the fluid onto the bottle to keep the pressure high within the bottle. Works well.
I would advice that you wash the bottle after you have completed your task! "re-cycled tea"
Similar Threads
-
Charging Split, Using Amps
By Robearbam in forum FundamentalsReplies: 16Last Post: 08-06-2011, 09:05 PM -
split system charging
By frankman in forum Air ConditioningReplies: 8Last Post: 15-11-2010, 03:24 PM -
charging split systems
By frankman in forum Air ConditioningReplies: 3Last Post: 20-08-2010, 10:28 PM -
split inverter unsure of proper charge spec.. how to charge?
By cadillackid in forum Air ConditioningReplies: 4Last Post: 19-11-2009, 01:52 PM -
Cold weather charging
By FEISTY in forum Tools and CalculatorsReplies: 11Last Post: 27-02-2009, 08:14 AM