    Coil Cleaning - Heating so slightly OT



    Haven't seen the problem yet but apparently we have a large(ish) air handling unit which has had poor filter maintenance on it the LPHW heating coil is badly blocked on the airside.

    Any suggestions on the best way to get it clean again?

    Bearing in mind that the AHU probably won't have a duct drain adjacent to the coil our first thought of a pressure washer may have to go on the back burner for the time being.

    Does anyone know of a good cleaning chemical that would shift several years worth on baked on dust and dirt?

    Coil is copper I believe.


    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  2. #2
    Join Date
    Jun 2010
    Location
    Yorkshire
    Age
    59
    Posts
    520
    Rep Power
    19

    Re: Coil Cleaning - Heating so slightly OT

    Can you get the filter out. Soak in hot soapy water maybe then reverse blow off with OFN.

  3. #3
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Coil Cleaning - Heating so slightly OT

    Hey Brian
    I had a similar problem recently and got a product from Gasco i think called zip clean ,

    its an aerosol foaming spray that doesn't require flushing afterwards.
    Just whack it on ,let it gobble away an hoover up the crap afterwards. Handy stuff if drainage is a problem

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: Coil Cleaning - Heating so slightly OT

    ^^ Thanks guys, they've got the filter remains out already and making new frames for some new filters.

    I was thinking about a foam, I'll look that one up, thanks.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: Coil Cleaning - Heating so slightly OT

    The other alternative is to remove the coil from the AHU if this is possible, and then pressure wash to your hearts content.

    We're going around at the moment removing burst LPHW frost coils from AHU's and carrying out on-site brazing repairs.....

    Roll on Thursday when the cold weather returns.....loads more work
    Last edited by frank; 14-12-2010 at 08:47 AM.

  6. #6
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,853
    Rep Power
    46

    Re: Coil Cleaning - Heating so slightly OT

    I've had a few cellar cooler coils that have blocked up, one we removed and pressure washed outside, another i made a chute out of a tarpaulin to catch the water and direct it into one of those big gorilla tubs/buckets and washed it out with some coil cleaner and rinsed.

    Have found an air line with a propper blow gun good at cleaning dust and straw out of condensers on farms when customer has been bright enough to install stuff in the loft, only down side is you get covered in dust.

    Jon

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: Coil Cleaning - Heating so slightly OT

    Actually went to site today for a look-see.

    Crap, that kit is old... It's a air supply fan for a swimming pool built around the time that Noah took up swimming lessons.

    I had thought, before arrival, of removing the coil - hah, no chance. I was stood next to the section with the coils in. Two coils back to back, frost and reheat mounted horizontally.

    Size, about 2.5m square, case constructed out of 1/4 plate by the looks of it and with enough services running around to provide the odd space to get a pair of steps through.

    Under the coil deck, a good 9 feet under, in a hole in the plant room floor is the fan section. Now that's held together with hardboard, plywood and gaffer tape. It just keeps getting better.

    Anyway, found the ladder to put down the hole to reach above the hole and prise open an old filter access door.

    Do you know, things might be looking up after all. It looks like the crud on the coil face is actually pieces of rusted metal that have been falling off the various bits of tin that were the frame for the filters. So I might get away with a simple vacuum cleaner job.

    Still a sh!te job but there you go.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  8. #8
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Coil Cleaning - Heating so slightly OT

    "If in doubt - Biff it out"
    Saying of Ex Prescold service manager

  9. #9
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: Coil Cleaning - Heating so slightly OT

    ^^ Quite right too ^^

    Anyway got the job done today.

    Luckily the ductwork contractor was on site preparing a large access plate and new filter frames. He fitted it and then removed it so I had a decent sized hole to work through.

    Filled up two vacuum cleaner, Henry, bags with the crap of the coil face; rusty metal, fluff, seagull feathers you know the sort of thing.

    A good spray with some Pro-Clean and it doesn't look too bad allowing for the partially corroded fins due to sea air.

    Mind you, you could hear the fan coming on load as the coil was cleaned.

    Usual good working area though, stood on tiptoe on the top of my steps working through a 1ft, 300mm, gap between pipes and the unit.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Similar Threads

  1. Simple off-coil temperature for Fan Coil Unit in Heating.
    By robertheppell in forum Fundamentals
    Replies: 11
    Last Post: 20-05-2009, 06:26 AM
  2. pressuer drop across heating coil
    By krratheeshnair in forum Air Conditioning
    Replies: 4
    Last Post: 08-05-2009, 08:38 PM
  3. LG heat pump problem
    By back2space in forum Heat Pumps
    Replies: 132
    Last Post: 01-02-2009, 11:23 PM
  4. heating coil or cooling coil?
    By botching in forum Air Conditioning
    Replies: 8
    Last Post: 09-06-2008, 08:37 PM
  5. heating coil in front of duct unit
    By cruzeiros in forum Air Conditioning
    Replies: 3
    Last Post: 13-02-2006, 11:32 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •