Legionnaires' disease & hot water systems
I'm currently undertaking a study into Legionnaires' Disease and hot water systems.
Over the years, a number of my Australian & NZ colleagues have explained that Australian ?law? requires hot water, in storage, to be heated about 62'C for a certain time period - once per ?week?.
If anyone has literature to hand, or links, which can direct me towards these legal requirements &/or recommendations, I'd be most grateful.
Thank you in anticipation.
Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
03-09-2010, 04:01 PM #2
Re: Legionnaires' disease & hot water systems
http://www.amm.co.uk/files/factsabout/fa_leg.htm
http://www.admin.ox.ac.uk/safety/UPS0707.shtml
Des, there are tons of papers on the internet.
My simple philosophy says that the more we protect ourselves - the more vulnerable we are.
-
03-09-2010, 04:05 PM #3
Re: Legionnaires' disease & hot water systems
desA, if you type the following link: www.hse.gov.uk & search for 'Legionella Approved Code of Practice L8 you can download for free.
Or the ISBN is: 9780717617722.
I passed my quals from this guide.
tmm
-
03-09-2010, 04:12 PM #4
Re: Legionnaires' disease & hot water systems
Thanks so much Chemi & tmm. Those are an excellent start.
So little really seems to be known in regards to this in regards to hot water systems in some countries. Apparently Australia & NZ have legislation that applies to heat-pumps as well. (To the best of my knowledge).Last edited by desA; 03-09-2010 at 04:16 PM.
Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
03-09-2010, 04:21 PM #5
Re: Legionnaires' disease & hot water systems
desA, in the UK to maintain compliance you must store at 60 & distribute at 50. If you read the guide the only temperature at which you kill ALL of the legionella is actually 70. Since you mention heat pumps you will instantly recognise the problem with flow temps at 45!
Don't start me on AWHP/GSHP's!
tmm
-
04-09-2010, 10:27 AM #6
Re: Legionnaires' disease & hot water systems
Legionella is only dangerous when water is in contact with air. In a closed circuit for heating, legionella does not develop.
-
04-09-2010, 05:33 PM #7
Re: Legionnaires' disease & hot water systems
I know for Belgium that you not only have to heat the water to - I think - 65 °C on a regular base - how regular , I don't know - but it must then also flows through all the tap points. So you must install a loop the point most far away from the boiler and a pump on that loop.
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
04-09-2010, 05:47 PM #8
Re: Legionnaires' disease & hot water systems
Searched once fro Belgium and read in a thesis to obtain a Master degree.
Some highlights
You have low, medium and high risk installations.
Chemical desinfection not allowed, only heating
In Europe , the EWGLI group. (European WorkGroup Legionella Infections)
Additionally chemical is allowed
Waterhoses for fire not included but connected to a different waternet that is used only for fire.
Not necessary for private homes.
Practical experiences temp60 °C, 2 minutes flushing, then 65 °C and 1 minute flushing and finally 70 °C and 30 seconds.
Cold water lines always <25°C.
Warm water always >55°C and > 60°C when leaving boiler
When mixing, only 5 m tube length and < 3 l volume (clinics < 1 l)It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
05-09-2010, 06:21 AM #9
Re: Legionnaires' disease & hot water systems
Thanks so much Peter. Excellent review of the current status in Europe. This seems to be an emerging area - certainly of great interest to me.
If you are able to PM me details of the Master's Thesis you refer to, I'd be most grateful.Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
19-10-2010, 07:47 PM #10
Re: Legionnaires' disease & hot water systems
Hi there doing water quality at work myself. Document called L8 you will be able to download from net. Water coming from tap should be at least 50 deg C after 1 minute of running and should return to hot tank at 55 deg C. Shower heads, shower taps and dead legs have to be flushed once a week.
-
13-12-2010, 07:40 PM #11
Re: Legionnaires' disease & hot water systems
In Germany there is a bunch of standards regarding preventing legionella. Legionellas are dangerous only when it is breathed.
ALso, it is not just the heating up to the certain temperature. If water content in the pipes is more than 3 liters, than there is a need for a recirculation or if loop system is used, than there is no need for a recirculation pipeline. Which system is installed? If you have a big project, than take care about it, if not, be COOl
-
13-12-2010, 07:51 PM #12
Re: Legionnaires' disease & hot water systems
Thanks for the information.
Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
Similar Threads
-
Advice required Air / Water heat pump systems
By oddjob1607 in forum Heat PumpsReplies: 8Last Post: 13-12-2010, 07:48 PM -
Hoshizaki Ice Maker
By Abe in forum Legal-Business-MarketingReplies: 19Last Post: 01-05-2010, 03:27 AM -
Fact or Fiction
By david.findlay in forum FundamentalsReplies: 40Last Post: 09-03-2009, 06:19 PM -
My local Apprentice Training Classes
By shogun7 in forum TrainingReplies: 12Last Post: 17-03-2007, 03:10 PM -
Building a wine cabinet
By Rory in forum Technical DiscussionsReplies: 38Last Post: 13-07-2004, 08:28 PM