    Hello everyone,

    I installed a multisplit system with two indoor units (PLA-RP71BA2)

    and the outdoor unit is PUHZ-RP140VHA2.

    The power for the indoor units is fed from the outdoor unit.

    Everything is switched on but there is no power being sent to the remote controller PAR-21MAA.

    Looking at an indoor circuit board there are 3 LEDS.

    LED 1 is on showing there is power to the indoor unit.

    LED 2 is off which means no power being sent to remote controller.

    LED 3 is flashing which indicates communication to the outdoor unit.

    What could be the cause of not sending power to the remote controller?

    Thanks in advance for any help.



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Mitsubishi Remote controller Par21-MAA has no power

    power off and switch all the dip switches to the opposite position then back again then re power up-the dip switch positions are in the correct position but poor contact.

  3. #3
    Join Date
    Nov 2008
    Location
    London
    Posts
    11
    Rep Power
    0

    Re: Mitsubishi Remote controller Par21-MAA has no power

    Thanks for the quick reply. Are you referring to dip switches on the indoor unit circuit board?

    Or are there dipswitches on the remote controller as well?

    Thanks.

  4. #4
    Join Date
    Nov 2008
    Location
    birmingham
    Posts
    155
    Rep Power
    19

    Re: Mitsubishi Remote controller Par21-MAA has no power

    dipswitches on the indoor unit

  5. #5
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: Mitsubishi Remote controller Par21-MAA has no power

    hi tek2k

    Do You Get anything at all at the remote like the LED screen trying to start?

    How have you wired the remote controller cable have you wired from remote controller to AC1 to AC2? a daisy chain effect?

    cheers lee

  6. #6
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Mitsubishi Remote controller Par21-MAA has no power

    indoor dipswitches-on a twin split u only wire par21 to 1 unit. s1-s3 is linked

  7. #7
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: Mitsubishi Remote controller Par21-MAA has no power

    hi install monkey,

    yeah only run 0.75 cable from remote to one unit only i have done this before running it daisy chain and remote will not start up

  8. #8
    Join Date
    Jul 2009
    Location
    stoke on trent
    Posts
    48
    Rep Power
    0

    Re: Mitsubishi Remote controller Par21-MAA has no power

    make sure you've wired the par21 to the master only, make sure you have both indoor isolators on before you power up the condenser, check you have 12vdc at the remote

  9. #9
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: Mitsubishi Remote controller Par21-MAA has no power

    The indoor unit is showing that its not going to send 12 vdc to the remote controller with indoor circuit board LED 2 off for a reason.
    One reason could be that the outdoor unit is not set for refrigerant address 0.

    For example
    If you had a group of 3 twin splits in a shop & use one PAR21 then you would make the outdoor unit refrigerant address
    0= master unit
    1= 1st slave unit
    2= 2nd slave unit.

    Only the indoor unit connected to the master outdoor unit with address 0
    will power up 12v dc to the PAR21.

    Normally outdoor units come out of the factory all set for refrigerant address 0. So systems normally work out of the box as stand alone split systems becuse the indoor circuit board can see that it is connected to the master outdoor unit address 0 so the indoor board knows it has to power up the remote controller with 12vdc.

    Suggest double check outdoor unit address setting = 0
    If thats ok & interconneting S1, S2, S3 or all connected correctly & power supply voltage is correct then suspect outdoor circuit board problem.

  10. #10
    Join Date
    Nov 2008
    Location
    London
    Posts
    11
    Rep Power
    0

    Re: Mitsubishi Remote controller Par21-MAA has no power

    Ok will try all the above. Thank you for the input. I will report back on the solution.

  11. #11
    Join Date
    Dec 2005
    Location
    Cheshire
    Age
    39
    Posts
    264
    Rep Power
    21

    Re: Mitsubishi Remote controller Par21-MAA has no power

    Quote Originally Posted by tek2k View Post
    Ok will try all the above. Thank you for the input. I will report back on the solution.
    Also check the master indoor board. I've had a SLZ-KA50stand alone split once no power to controller, the connection pin on the pcb board was disconnected. (think its a blue cable CN2 or something)

  12. #12
    Join Date
    Nov 2008
    Location
    London
    Posts
    11
    Rep Power
    0

    Re: Mitsubishi Remote controller Par21-MAA has no power

    Hello just to let you guys know I clicked the dip switches on SW1 on the outdoor unit back and forth once making sure they were all 0 and turned back on and LED 2 lit up and remote was working fine.

    Thanks for the help.

  13. #13
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Mitsubishi Remote controller Par21-MAA has no power

    Quote Originally Posted by tek2k View Post
    Hello just to let you guys know I clicked the dip switches on SW1 on the outdoor unit back and forth once making sure they were all 0 and turned back on and LED 2 lit up and remote was working fine.

    Thanks for the help.
    i wont give up my day job yet!

Similar Threads

  1. mitsubishi start up
    By ballvalve in forum Air Conditioning
    Replies: 12
    Last Post: 21-01-2011, 06:12 PM
  2. Toshiba RAV-240KR(W) - replacement remote controller?
    By YC10 in forum Air Conditioning
    Replies: 2
    Last Post: 06-10-2010, 09:47 PM
  3. Mitsubishi Remote
    By ronaldo9 in forum Air Conditioning
    Replies: 1
    Last Post: 17-06-2010, 09:13 AM
  4. Another mitsubishi weird one
    By marc5180 in forum Air Conditioning
    Replies: 5
    Last Post: 10-08-2009, 07:31 PM
  5. SR2 50 models electric SBY diagonostics made simple
    By absolute-zero in forum Transport
    Replies: 5
    Last Post: 04-01-2008, 05:11 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •