    Airedale Cus5



    Having a problem with some of these condensing units, air off seems to be exiting horizontally rather than vertically, looking at fitting fan assembly from another model...

    Has anyone experienced this, if so any advice?

    units are located in same compound and are recircing air onto each other.

    al



  2. #2
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    20

    Re: Airedale Cus5

    Ive had a few fan speed controller go on these thats about it

    could it be possible to fit a cowl to force air up wards?
    Paul


    "KEEP IT COOL"

  3. #3
    Join Date
    Sep 2008
    Location
    england
    Posts
    427
    Rep Power
    20

    Re: Airedale Cus5

    Just an idea here, might be complete b******s but could the fans be running the wron way.

  4. #4
    Join Date
    Dec 2007
    Location
    Birmingham
    Age
    69
    Posts
    38
    Rep Power
    0

    Re: Airedale Cus5

    Quote Originally Posted by al View Post
    Having a problem with some of these condensing units, air off seems to be exiting horizontally rather than vertically, looking at fitting fan assembly from another model...

    Has anyone experienced this, if so any advice?

    units are located in same compound and are recircing air onto each other.

    al
    Always the same with Airedale Cus.
    When the fan is in control (holding the discharge pressure at the correct setting ) the fan air discharge is vertical.

    When the fan motor is at its maximum speed you will find that the condenser air discharge is thrown to the side of the Cu and you get the hot air recirculating onto the condenser face.

    Many times i have had to make up baffle plates between Cu's to stop this recirce happening.
    On one of the jobs we fabricated 1ft high circular plates which bolted around the condenser fan frame using the fan bolts to hold them in place.
    This did stop the air being blown sideways from the unit.
    but it does cause some pressure on the fan, you still fail to get the air to flow up vertical.

    On the older Cu units when there used to be a separate motor and a metal blade, Airedale could supply different fan blades which were for high ambient conditions.
    I do not know if this is possible with there newer design of condenser fan.

    Best of luck

    Bob

  5. #5
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,451
    Rep Power
    41

    Re: Airedale Cus5

    Lads

    thanks for the fast responses, i did notice that a larger capacity unit didn't have this problem and i'm wondering if i could retrofit these fans instead?

    I think it was a cus10, are the condenser fans the same diameter across the range?

    thanks again guys

    al

  6. #6
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,451
    Rep Power
    41

    Re: Airedale Cus5

    Hi Glenn

    they are single phase fans all running correct, thanks for asking though

    al

  7. #7
    Join Date
    Oct 2007
    Location
    Northamptonshire
    Age
    60
    Posts
    25
    Rep Power
    0

    Re: Airedale Cus5

    try cleaning the condenser (if it only happens at high fan speed)

  8. #8
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,451
    Rep Power
    41

    Re: Airedale Cus5

    Hi Fixaman

    Condensers are fairly clean

    al

  9. #9
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: Airedale Cus5

    The problem you are having is universal with that specific fan configuration i.e. a plate fan on a flat surface. The effect of the air "deflecting" out the sides is greatly influenced by rpm. Normally the short cycling air doesn't impede the performance but if it is then perhaps a short length of circular duct or spigot will cure what ails thee.
    Quidvis Recte Factum Quamvis Humile Praeclarum.

    Latine dictum, sit altum videtur.

    Si hoc comprehendere potes, gratias age magistro Latinae.

  10. #10
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,451
    Rep Power
    41

    Re: Airedale Cus5

    Trash

    I think that's the answer!!

    Thanks everyone

    Al

  11. #11
    Join Date
    Dec 2008
    Location
    UK
    Posts
    563
    Rep Power
    24

    Re: Airedale Cus5

    The short section of air discharge ducting should be kept to about 300mm in height and for ease of construction it can be a simple cylinder in shape or can be an outwards funnel shape if you wish to get a little more complicated.

  12. #12
    Join Date
    Oct 2007
    Location
    Northamptonshire
    Age
    60
    Posts
    25
    Rep Power
    0

    Re: Airedale Cus5

    Just clean the condenser and it will work correctly

  13. #13
    Join Date
    Mar 2008
    Location
    United Kingdom
    Posts
    1
    Rep Power
    0

    Re: Airedale Cus5

    Had this problem many times in the past, give the condensers a damn good clean, they may look ok on the outside but will be restricted internally.

  14. #14
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: Airedale Cus5

    whats the best way to clean these condensors coils?

    i usually use a solution called enviro coil mixed with water and spray it on to the coil by use of a small garden hozelock pump, i find that using this gets some of the dirt off the coil but i am sure there must be a better way of cleaning the coil more thouroghly.

    i have once used a pressure washer on the coils and that was really good however when the units are on a roof or access is limited that could be tricky.

    whats so you guys do?

    Also anyone hve any details on these condensors like wiring diagrams and refrigerant charge?

    cheers lee
    Last edited by moondawn; 02-12-2010 at 10:19 PM.

Similar Threads

  1. Airedale controller
    By boulting in forum Air Conditioning
    Replies: 8
    Last Post: 27-09-2009, 08:53 PM
  2. hunting expansion valve on airedale c/control
    By knight rider in forum Technical Discussions
    Replies: 28
    Last Post: 10-07-2009, 11:21 PM
  3. Airedale Chiller
    By pavilion in forum Air Conditioning
    Replies: 2
    Last Post: 22-01-2009, 08:22 AM
  4. Fault on an Airedale unit
    By marc5180 in forum Air Conditioning
    Replies: 50
    Last Post: 30-06-2007, 06:10 PM
  5. airedale
    By marley821 in forum Air Conditioning
    Replies: 2
    Last Post: 24-03-2006, 08:07 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •