    Mop expansion valve



    Hi guys.can someone tell me if i can install a mop txv together with a CPR valve.stuck on a job with none a normal txv at present and the previous txv gone bad on that walk in freezer and its got a CPR valve on it.Help will be apriciated.Thanks



  2. #2
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Mop expansion valve

    1) What is the evaporating temperature you need at the outlet of the aircooler?

    2) What's the MOP value. If this value is below the evaporating temperature the aircooler will not be fed.
    To make progress is never good enough, I want to do better and better and better

  3. #3
    Join Date
    Feb 2010
    Location
    NT
    Posts
    66
    Rep Power
    15

    Re: Mop expansion valve

    -40 to -15 deggree celcius on the mop and between -20 to -26 on the evaporator outlet.

  4. #4
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Mop expansion valve

    Quote Originally Posted by ironmen View Post
    -40 to -15 deggree celcius on the mop and between -20 to -26 on the evaporator outlet.
    About the TEV you have gave me the range of evaporating temperatures. The MOP is defined only by a unique value specific to that valve.

    -20 to -26ºC, before the CPR or downstream the valve?
    To make progress is never good enough, I want to do better and better and better

  5. #5
    Join Date
    Feb 2010
    Location
    NT
    Posts
    66
    Rep Power
    15

    Re: Mop expansion valve

    I was away for a little while.In the evaporator inlet after the txv.

  6. #6
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Mop expansion valve

    The CPR does the job that the MOP TXV will be trying to do. In my view, I'd keep it simple & use a standard TXV.

    At worst, though, a TXV with a very high MOP setting (above CPR setting) would probably not interfere too much.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  7. #7
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Mop expansion valve

    Quote Originally Posted by desA View Post
    At worst, though, a TXV with a very high MOP setting (above CPR setting) would probably not interfere too much.
    I also agree, but if MOP is -25ºC probably it will have lack of feeding.
    To make progress is never good enough, I want to do better and better and better

  8. #8
    Join Date
    Feb 2010
    Location
    NT
    Posts
    66
    Rep Power
    15

    Re: Mop expansion valve

    Thanks guy.Got a normal txv put it in and its working all good.600 k to get one.Did not want to put that mop in.Thanks to reply.

Similar Threads

  1. Lg mps system ( expansion valve location)
    By hussain2002cab in forum Air Conditioning
    Replies: 6
    Last Post: 18-03-2010, 10:19 PM
  2. Actual Expansion Valve Process
    By AastroGuru in forum Fundamentals
    Replies: 11
    Last Post: 03-02-2009, 09:53 AM
  3. Setting of Hand expansion valve
    By Iceehot in forum NH3
    Replies: 7
    Last Post: 10-09-2008, 01:25 AM
  4. the function of the electronic expansion valve
    By Crystal-426 in forum Fundamentals
    Replies: 10
    Last Post: 22-06-2008, 12:29 PM
  5. Need Divine Intervention - plugged drier or expansion valve?
    By archibaldtuttle in forum Trouble Shooting
    Replies: 4
    Last Post: 08-06-2008, 06:52 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •