Results 1 to 8 of 8
Thread: Mop expansion valve
-
18-11-2010, 12:25 PM #1
Mop expansion valve
Hi guys.can someone tell me if i can install a mop txv together with a CPR valve.stuck on a job with none a normal txv at present and the previous txv gone bad on that walk in freezer and its got a CPR valve on it.Help will be apriciated.Thanks
-
18-11-2010, 01:59 PM #2
Re: Mop expansion valve
1) What is the evaporating temperature you need at the outlet of the aircooler?
2) What's the MOP value. If this value is below the evaporating temperature the aircooler will not be fed.To make progress is never good enough, I want to do better and better and better
-
18-11-2010, 09:52 PM #3
Re: Mop expansion valve
-40 to -15 deggree celcius on the mop and between -20 to -26 on the evaporator outlet.
-
19-11-2010, 09:06 AM #4
Re: Mop expansion valve
To make progress is never good enough, I want to do better and better and better
-
26-11-2010, 04:39 AM #5
Re: Mop expansion valve
I was away for a little while.In the evaporator inlet after the txv.
-
26-11-2010, 07:38 AM #6
Re: Mop expansion valve
The CPR does the job that the MOP TXV will be trying to do. In my view, I'd keep it simple & use a standard TXV.
At worst, though, a TXV with a very high MOP setting (above CPR setting) would probably not interfere too much.Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
26-11-2010, 08:58 AM #7
-
28-11-2010, 01:29 PM #8
Re: Mop expansion valve
Thanks guy.Got a normal txv put it in and its working all good.600 k to get one.Did not want to put that mop in.Thanks to reply.
Similar Threads
-
Lg mps system ( expansion valve location)
By hussain2002cab in forum Air ConditioningReplies: 6Last Post: 18-03-2010, 10:19 PM -
Actual Expansion Valve Process
By AastroGuru in forum FundamentalsReplies: 11Last Post: 03-02-2009, 09:53 AM -
Setting of Hand expansion valve
By Iceehot in forum NH3Replies: 7Last Post: 10-09-2008, 01:25 AM -
the function of the electronic expansion valve
By Crystal-426 in forum FundamentalsReplies: 10Last Post: 22-06-2008, 12:29 PM -
Need Divine Intervention - plugged drier or expansion valve?
By archibaldtuttle in forum Trouble ShootingReplies: 4Last Post: 08-06-2008, 06:52 PM