    ice formation on cooling coil



    Respected sir
    the problem which im facing from few days is the ice formation on cooling coil with the 45ps suction and 200 psi discharge pressure, i did replace the expansion valve too but not succeded refrigerant is 407c. pls let me know the standerd parameter for 407c air conditioning units.we are using daikin air conditioning unit.

    if we not use a equalising line to thermostatic expansion valve is any problem for compressor ?

    i hope u wil give a postive reply



  2. #2
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: ice formation on cooling coil

    Hi there,

    Your suction pressure is low. Suction for air conditioning wit R407C should be around 60Psi(g).
    Your TEV must have external equalizing line otherwise you will have a problem (high superheat and starved evaporator).

    Cheers
    Even Einstein Asked Questions

  3. #3
    Join Date
    Feb 2010
    Location
    Ireland
    Age
    38
    Posts
    82
    Rep Power
    15

    Re: ice formation on cooling coil

    Are you using daikin indoor and out door? Or is it on a coil in an ahu?

  4. #4
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: ice formation on cooling coil

    Your discharge pressure also seems low.

    Does the condensor fan have a fan speed controller? Maybe try adjusting to increase the head pressure.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  5. #5
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: ice formation on cooling coil

    Heat absorbed + heat of compression = heat rejected.

    If little heat is being absorbed, then little heat will be rejected. IOW, if the evap is not picking up a normal load (which seems to be the case), then the condenser TD will be low.

    We would need a lot more information to determine why the evap is not picking up a normal load.

  6. #6
    Join Date
    Sep 2010
    Location
    England
    Posts
    40
    Rep Power
    0

    Re: ice formation on cooling coil

    Pressures are to low for R407C,like KTM said is it both Daikin indoor/outdoor or connected to an AHU.
    Are you measuring the true Discharge Pressure or on the service ports of the condenser, which would be suction and expansion line.

  7. #7
    bats100's Avatar
    bats100 Guest

    Re: ice formation on cooling coil

    I have one coffin freezer consisting 4 12 feet Hill cases Model NZ 120 serial numbers 3756-271,272,273,274.
    they are fused together back to back.
    one copeland compressor is working in back bone.
    in other words its one case back to back.
    during defrost cycle, which is stricktly on time based defrosts. 2 freezers are not getting any defrost. but other 2 are defrosting fine. I checked and found that heating element(solid u shape) that is fit on side of fins is not getting hot during defrost.
    i read that thermoswitch or thermosensors might be bad, i would like any help on what to look or test first and position of sensors if involved.
    i am not professional as rest of team is but can apply your expertise for sure.
    thanks for ur time..

  8. #8
    javed's Avatar
    javed Guest

    Re: ice formation on cooling coil

    assalamu- alaikum sir.
    you check expansion valves bulb and cooling coil finks, fan motor rotation , evaporator fan speed and machine return air flow .
    and last drier filter.
    inshallha your problem will solve .

  9. #9
    Join Date
    Mar 2005
    Location
    edinburgh
    Age
    51
    Posts
    10
    Rep Power
    0

    Re: ice formation on cooling coil

    get the head pressure up!!!adjust fan speed controller.

Similar Threads

  1. indoor split ice
    By SkyWalker in forum Air Conditioning
    Replies: 5
    Last Post: 07-09-2009, 04:51 PM
  2. heating coil or cooling coil?
    By botching in forum Air Conditioning
    Replies: 8
    Last Post: 09-06-2008, 08:37 PM
  3. removing humidity
    By Sledge in forum Air Conditioning
    Replies: 31
    Last Post: 22-06-2007, 05:40 AM
  4. Cooling Coil question
    By hvacn00b in forum Air Conditioning
    Replies: 25
    Last Post: 13-09-2006, 01:00 AM
  5. water cooling coil
    By Lc_shi in forum Fundamentals
    Replies: 11
    Last Post: 02-09-2006, 08:45 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •