    Hi All!
    Change R22 with R 422D and a few days later
    disappeared from the oil and do not open the
    EXV.
    30 GH pro dialog plus

    Thanks



  2. #2
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Expansion valve

    Quote Originally Posted by Newser View Post
    Hi All!
    Change R22 with R 422D and a few days later
    disappeared from the oil and do not open the
    EXV.
    30 GH pro dialog plus

    Thanks
    Hi
    what is the alarm that the controller shows??
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  3. #3
    Newser's Avatar
    Newser Guest

    Re: Expansion valve

    Hi.

    44, 46, I think superheat the problem ....perhaps?
    How do I change this in the settings?

  4. #4
    Join Date
    Jun 2006
    Location
    South Coast
    Posts
    278
    Rep Power
    24

    Re: Expansion valve

    Your problem is the refrigerant, the chiller is configured for R22. R422D is not recommended for flooded coolers and EXV's plus if you are still using mineral oil you will have oil return problems.
    The temperature glide is quite high as well on R422D at water temperatures of 6C
    Suggest you go back to R22

  5. #5
    Join Date
    Jan 2009
    Location
    Australia
    Age
    60
    Posts
    108
    Rep Power
    16

    Re: Expansion valve

    Gibbo's right. You can't do much with the french machines. You have 2 choices. Change the controls and put in aftermarket exv's and set them up for 422 ( you'll probably lose some capacity) or go back to R22. I know which one of these is the cheapest.

  6. #6
    Newser's Avatar
    Newser Guest

    Re: Expansion valve

    Thank for All.

    The expanxion valve operation can be changed?
    Aftermarket EXV may be a problem.

  7. #7
    Newser's Avatar
    Newser Guest

    Re: Expansion valve

    And one more question...what is proposed instead of R22?

    Thx

  8. #8
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,453
    Rep Power
    41

    Re: Expansion valve

    R422D is fine, but you must change the oil to synthetic, mineral oil will not return with 422d, oil is probably sitting in the evaporator. Maybe refit r22 and return oil to compressor then replace with synthetic oil and then charge 422d.

    alec

  9. #9
    Join Date
    Jun 2006
    Location
    South Coast
    Posts
    278
    Rep Power
    24

    Re: Expansion valve

    And the reason you believe your statement to be true is.

Similar Threads

  1. Replies: 3
    Last Post: 09-05-2009, 03:17 AM
  2. Actual Expansion Valve Process
    By AastroGuru in forum Fundamentals
    Replies: 11
    Last Post: 03-02-2009, 09:53 AM
  3. Setting of Hand expansion valve
    By Iceehot in forum NH3
    Replies: 7
    Last Post: 10-09-2008, 01:25 AM
  4. the function of the electronic expansion valve
    By Crystal-426 in forum Fundamentals
    Replies: 10
    Last Post: 22-06-2008, 12:29 PM
  5. Need Divine Intervention - plugged drier or expansion valve?
    By archibaldtuttle in forum Trouble Shooting
    Replies: 4
    Last Post: 08-06-2008, 06:52 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •