Thread: open plan problem
-
14-10-2010, 03:19 PM #1
open plan problem
Hey guys my problem is this:
open plan office cut into four zones, a daikin controller for each zone i try to maintain the temp between 21-22
im aware that the airflow can come out as low as 14 and as high as 25 now the problem is when the systems are cooling air coming out is making ppl too cold obviously because it coming out at 14 until office is cooled. I cannot find a solution please help!!!!
what if i just put on manual heating at 17 or 18 degrees that would irradicate the cooling ???
-
14-10-2010, 03:32 PM #2
Re: open plan problem
hi andy , can you tell us the heating + cooling set point . and what is the situation with the fresh air intake ?
-
14-10-2010, 03:37 PM #3
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: open plan problem
You are chatting here. Please describe problem as engineer and not as some youngster on Facebook.
-
14-10-2010, 03:42 PM #4
Re: open plan problem
get of your high horse mate you are in no position to tell ppl how to type grow up
Last edited by frank; 14-10-2010 at 06:53 PM. Reason: personal comment removed
-
14-10-2010, 04:02 PM #5
Re: open plan problem
cooling set point is 21 and heating 22.fresh air intake of ahu s at 14.9 degrees with 47 humidity
-
14-10-2010, 05:56 PM #6
Re: open plan problem
what type of indoor units are they ducted,cassetes etc 14 degrees air off seems quite high daikin normaly work off a 12C delta T
-
14-10-2010, 06:49 PM #7
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: open plan problem
Last edited by nike123; 14-10-2010 at 06:58 PM.
-
14-10-2010, 09:02 PM #8
Re: open plan problem
Hi Andy, can you advise model numbers of the systems, may be able to help you further.
-
20-10-2010, 03:28 PM #9
Re: open plan problem
porblem solved thanks to all who replied anyway, the AHUs heating coils had no hot water supply due to boiler malfunction. its a shame there is individuals on here with a big ego an need to assert them selves by insulatin others and no we are not on the same level im 24 your 40 and you need to try and assert yourself with your over ego and ignorant behaviour no need to reply asshole.
-
27-10-2010, 07:51 AM #10
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Similar Threads
-
MFI AMP6855 defrost problem
By gliderpilot47 in forum DomesticReplies: 4Last Post: 12-01-2011, 12:11 PM -
Hitachi airconditioning problem
By mlaauwen in forum Air ConditioningReplies: 6Last Post: 14-07-2010, 05:28 PM -
problem with a small cooler
By corvairbob in forum Trouble ShootingReplies: 1Last Post: 03-03-2010, 05:19 AM -
Cooling problem with VRV REYQ24M7.
By cool#9 in forum Air ConditioningReplies: 3Last Post: 07-02-2010, 12:20 PM -
carrier vvt problem
By declan simmonds in forum Air ConditioningReplies: 4Last Post: 28-01-2009, 02:53 PM