    Exclamation York YR Soft Starter - HELP



    Hi All,
    I need some help Please!!
    I currently working on a York Screw Chiller YR series 150 with water cooled condenser and Flooded Evaporator. It has a large Frick Semi Hermetic.
    I work for another Manufacturers service Dept and have access to the York Bulletins etc. Amazing what a cup of Tea gets access to!
    The chiller suffered a Melt Down in the Motor terminal box.
    Now that all the Motor Terminals, Leads and Links have been replaced I have re-energised the control circuit and have an instant "Phase A SCR Shorted" Message on the Optiview Panel.
    I have followed the "York" bulletin test instructions to the letter and still am not able to make a conclusive decision as to wether the fault is in fact a faulty SCR or the LCSSS Logic Board.
    All recorded "Gate" tests show the resistance values to be within expected Tolerances.
    All tests carried out have been done at the panel with the motor leads disconnected using a Fluke77 Digital Meter. Can I use a "Megger" across T1-L1 @250v to check the SCR is Shorted?
    The motor windings are Balanced and Continuos and have 1000Ohm resistance to Earth at 500v. Working on this unit until now has been a pleasure, it seems really well put together. It`s sister chiller was saved from a similar meltdown by removing the Self Amalgamating tape at the terninal studs and a Re-torquing. First time in 6 years! And yes they were not much more than Hand Tight!! We have only just got the maintenance on these units.
    Any thoughts and suggestions of a technical nature would be greatly appreciated.
    Thanks,
    Rob
    PS: York Parts Department here in UK have been really helpfull and organised!!



  2. #2
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: York YR Soft Starter - HELP

    Hi
    check all scr and make sure they are not shorted ,then you can cancel this protection via the screen control board ,i would only do this if you are 100% sure the scr's are ok !!!
    if u need any more info i have all the york literrature regarding soft starters on this model.
    in my own case we had a faulty starter that actully all scr's were shorted so we fit an external soft starter that works fine .
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  3. #3
    Join Date
    Dec 2008
    Location
    UK
    Posts
    55
    Rep Power
    16

    Re: York YR Soft Starter - HELP

    Hi Goshen,
    How did you confirm that the SCR` were shorted. I have measured resistance between T1 and L1 on all the SCRs and have got quite a high resistance in both directions. Resistance in excess of 2800 ohms. When I turn the power on I get 238 volts between each L1 and earth terminal. The same as the T1 and earth.
    Also space here is very limited so I have no room for external soft starter.
    I have a local company on standby to rebuild the SCRs once I can confirm that they are shorted. The SCRs are also available as single Items from York-JCI.
    Cheers,
    Rob

  4. #4
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: York YR Soft Starter - HELP

    Quote Originally Posted by centrecipew View Post
    Hi Goshen,
    How did you confirm that the SCR` were shorted. I have measured resistance between T1 and L1 on all the SCRs and have got quite a high resistance in both directions. Resistance in excess of 2800 ohms. When I turn the power on I get 238 volts between each L1 and earth terminal. The same as the T1 and earth.
    Also space here is very limited so I have no room for external soft starter.
    I have a local company on standby to rebuild the SCRs once I can confirm that they are shorted. The SCRs are also available as single Items from York-JCI.
    Cheers,
    Rob
    HI :
    mail me i used yorks guide !
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  5. #5
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: York YR Soft Starter - HELP

    hi which starter model do you have

  6. #6
    Join Date
    Dec 2008
    Location
    UK
    Posts
    55
    Rep Power
    16

    Re: York YR Soft Starter - HELP

    Hi, The starter is a "York" LCSSS liquid cooled Soft Starter. FLA 400amps 50hz 400vlots.
    Cheers,
    Rob

  7. #7
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: York YR Soft Starter - HELP

    hi rob check your email

  8. #8
    Join Date
    Dec 2008
    Location
    UK
    Posts
    55
    Rep Power
    16

    Re: York YR Soft Starter - HELP

    Hi All Again,
    Following a return visit to site.
    I have tested the SCRs and found that they are NOT shorted.
    However the Gate Driver output is way out of the recomended resistance values.
    I am now almost certain that the Logic Board is at Fault.
    A call to JCI is in order to get a new one I Think.

    The Starter is a SSS14LCE-50B.

    Any further recomendations regarding further tests would be most appreciated.

    Have a good weekend all!
    Rob

  9. #9
    Join Date
    Dec 2008
    Location
    UK
    Posts
    55
    Rep Power
    16

    Re: York YR Soft Starter - HELP

    Hi Guys,
    Thanks for your replies and advice.
    The unit is now running. I reconnected the motor leads and energised the panel.
    No Faults appeared and the start sequence was initiated. YUP the bloody thing started and run with no problem at all.
    I wonder if the starter was in fault due to the windings being disconnected??
    Needless to say the customer is thrilled that no further expense is required.
    Once again thanks for the help and "Keep Chilling"
    Rob

  10. #10
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: York YR Soft Starter - HELP

    hi all, just a quick point
    has the cc heater been on long?
    on theses modern w- chillers do they have atemp sensor to detect if cch has been on ¿?

  11. #11
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: York YR Soft Starter - HELP

    Quote Originally Posted by sedgy View Post
    hi all, just a quick point
    has the cc heater been on long?
    on theses modern w- chillers do they have atemp sensor to detect if cch has been on ¿?
     hi
    Yes most of these units monitor oil temp and will delay the start until oil reaches set point
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

Similar Threads

  1. Reliable soft starter
    By michaelm in forum Industrial
    Replies: 8
    Last Post: 23-07-2010, 04:22 PM
  2. Cutler Hammer Soft Starter
    By iceman007 in forum Electrical
    Replies: 11
    Last Post: 26-05-2010, 04:56 AM
  3. Cooy or Cosy - Soft Starter
    By Lumpy2 in forum Technical Speculations
    Replies: 3
    Last Post: 05-04-2010, 11:57 AM
  4. SCR short in soft starter.
    By mrsparky in forum Electrical
    Replies: 0
    Last Post: 14-12-2007, 12:19 PM
  5. York Water cooled solid state starter?
    By Dave the Fridge in forum Trouble Shooting
    Replies: 6
    Last Post: 27-03-2007, 05:03 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •