    I have a VRVII-S that during heating operation will periodically stop one fan and drop the speed rather low on the second fan of the outdoor unit. This lasts for only a short bit – maybe 30-60 seconds and then both fans ramp back up to full speed. Indoor units continue to operate with blowers running during these periods. This can happen as frequently as 5 - 7 minutes. No fault codes are showing.


    In reviewing the service manual, it states that if the high side pressure is greater that 454psi the fans will drop from Step 8 (both fans at full RPM) to step 1 where one fan stops and the second fan drops to 250 RPM. Is it reasonable to assume that is the operation I am observing and is it an issue that it happens as frequently as 5 minutes apart? Is this a normal part of the heating operation?


    Thank you.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: VRV-S heating operation

    Yes, it is a means of capacity control.

    It reduces the amount of energy that the system can extract from the ambient air.

    You will find similar control methods used on split system heat pumps also.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Sep 2010
    Location
    England
    Posts
    40
    Rep Power
    0

    Re: VRV-S heating operation

    Does the compressor speed alter? If it does then it soiunds like it is going into a safety control to lower pressure tenperture so it does not tripo out.

  4. #4
    Join Date
    Oct 2007
    Location
    United States
    Posts
    213
    Rep Power
    17

    Re: VRV-S heating operation

    Quote Originally Posted by wozza View Post
    Does the compressor speed alter? If it does then it soiunds like it is going into a safety control to lower pressure tenperture so it does not tripo out.

    With the air noise from the fans running it is a hard to hear the compressor until the one fan has fully stopped and the second fan is down on step 1 - 250 rpm. And then, almost as soon as the fans are at that point they start back up to run at full speed. So, there is a very short period that I can hear the compressor. It may have been slowing - but hard to say with out any test instruments.

    Is this an operating condition that I should be concerned about or is it normal with the system managing it as it is supposed to?

    Thank you.

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Daikin vrv III heating fault
    By grovecoooling in forum Air Conditioning
    Replies: 1
    Last Post: 13-01-2010, 12:23 AM
  3. Modifying aricond. for heating, cooling and hot water
    By kimusabi in forum Technical Discussions
    Replies: 3
    Last Post: 10-10-2008, 07:28 AM
  4. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •