Results 1 to 13 of 13
    sighmon55's Avatar
    sighmon55 Guest
    Installation query - Ceiling Mounted Evaporators
    Please can somebody advise me as to what the industry "norm" is for fixings on ceiling mounted evaporators? I recently became involved in a case whereby a newly installed evaporator (single fan approx 25kg) came loose from it's fixings inside a walk in freezer. The installer had used 4 x .75inch self-tapping screws to ceiling mount. The freezer is standard design - aluminium skin, insulation and then outer skin.
    I thought the suggested fixing method was studding?
    Sep 2003
    ISRAEL
    72
    4,248
    Re: Installation query - Ceiling Mounted Evaporators
    We use special bolts that holds the evaporator firmly to the ceiling.
    Oct 2008
    newbury
    1,444
    Best practice: nylon threaded rod
    3,853
    Generally i like to use either nylon threaded rod on small evaporators and stainless steel on big ones. Something to keep in mind is it needs to be able to hold the evaporator up if it becomes full of ice which could be anything from a few kilos to a few tons.
    One of the companies i subbie for has wooden beams built in to the roof panel where the evaporator is going to be sited and uses coach screws. This is because there is often no access to the roof to fit rods in the small shops he specialises in.
    It would also be worth checking the manufactures recommendations.
    Jon
    Apr 2008
    Southampton, England
    49
    1,023
    Nylon studding as Mr B and Monkey suggest.
    The nylon is used to alleviate hygiene and corrosion issues I believe. Using 4" screws eh? Well depending on the thickness of insulation the screws may only have gone through 1 skin. If they went through both then best not kneel on the top fixings unless your name is Officer Murphy. Doubt if the coldroom skin is designed (thick enough) to hold that weight anyway. Bad job.
    Cheers,
    Andy
    sighmon55's Avatar
    sighmon55 Guest
    Does anybody know where/if there is any "industry guidelines" on this type of install?
    sighmon55's Avatar
    sighmon55 Guest
    I presume this method involves drilling through from topside all the way into the freezer - Certainly seems a secure method equivalent to standard studding.
    Oct 2003
    5,630
    Drilling through the panels will give you cold-bridges.
    If you tighten firmly a bolt-through evaporator, you will have a small crater on the roof of the freezer (under the bolt/washer)where the condensed water will collect.
    Therefore, the nylon threads like Richard proposed solves this problem.
    We mostly slide a small piece of Armaflex over the bolts and glue it.
    sighmon55's Avatar
    sighmon55 Guest
    Going back to the original query - I presume using small (.75 inch) self-tappers in this case is a no no?
    Oct 2003
    5,630
    The original installer must attach his units in such a way that they under normal conditions can't fall from the ceiling, whatever method he wants to use for this.
    In your case, the evaporator fas fallen from the ceiling under normal conditions, so he failed to accomplish standard, safe requirements.
    If this should be a case for The Court, then I should take the install instructions of the manufacturer, measure the predrilled holes in the evaporator, and try to find how much load you can hang on a screw.
    Oct 2003
    5,630
    Jun 2001
    N.Ireland
    1,630
    Hello Gents
    In my case I use stainless steel treaded rod up through the ceiling to cross beams suspended from the main building structure, with aramaflex sealed over the rods with silicone.
    Small rooms can have the coolers supported by unistrut run above the room wall to wall with treaded rod dropped down through the ceiling. If you space the unistrut off the ceiling panel you can add some armaflex to the rod to stop cold bridging or sweating.
    Screws unless stainless rust and break, ceiling panels have no support normally for you to fix anything to
    Kind Regards Andy D
    Feb 2008
    adelaide sth.oz
    1,015
    i use 100mm square plates under the nut and washer with a liberal coating of silicone under the plate and around the threaded rod.good vapour seal and stronger support
  1. B& Q airforce ceiling mounted corner unit
    By bossblue in forum Air Conditioning
    Last Post: 25-07-2010, 04:54 PM
  2. ceiling mounted remote control for split A/C units
    By stevethebungee in forum Air Conditioning
    Last Post: 27-04-2010, 09:01 PM
  3. Hitachi Ceiling Mounted Indoor Unit Defect
    By Daikin=Overated in forum Air Conditioning
    Last Post: 06-11-2007, 08:49 PM