fujitsu ducted condensation control nightmare
I have 2 units Fujitsu ARY 60 UUAK / AOY 60 UMAYT with same problem - from time to time it goes to high pressure alarm. After a while get high pressure switch shortcircuited. I observed what is going on, and measured pressures. On outdoor unit fans start at low speed, and high speed is switched on at 37 bar. I think high speed should be switched earlier. What is reason for this? Electronics fault, program or sensor.
Last edited by gille; 13-10-2010 at 01:40 PM.
-
12-10-2010, 12:14 PM #2
Re: fujitsu ducted condensation control nightmare
Hi Gille,
in cooling mode speed of outdoor fan set ambient thermistor. Can be an ambient temperature became low +5C?
-
15-10-2010, 01:07 PM #3
Re: fujitsu ducted condensation control nightmare
You are right, I'll have to check thermistor, but I do not have ohm/temp table, maybe i could try to relocate thermistor.
Thank you.
-
15-10-2010, 02:02 PM #4
Re: fujitsu ducted condensation control nightmare
see http://www.refrigeration-engineer.co...0&postcount=26
Nike123 worked hard for me)
Similar Threads
-
Fujitsu AOT45 Split Ducted PCB ISSUES
By bobby 14 in forum Air ConditioningReplies: 5Last Post: 27-11-2010, 07:42 AM -
Fujitsu AOY24... ducted question
By Andy_WSM in forum Air ConditioningReplies: 51Last Post: 19-10-2010, 10:43 PM -
on/off switch contact for Fujitsu ducted AC
By paulsev in forum ElectricalReplies: 3Last Post: 02-12-2009, 10:23 PM -
fujitsu control mind of own
By leegally1983 in forum Air ConditioningReplies: 2Last Post: 26-09-2008, 11:55 PM -
AOT30 Fujitsu ducted air con
By oyama1965 in forum Trouble ShootingReplies: 2Last Post: 28-08-2008, 07:16 PM