Results 1 to 11 of 11
Thread: ice build up on suction return?
-
12-10-2010, 09:21 AM #1
ice build up on suction return?
Hi there,
I have just taken over a maintenance contact of a blast freezer 45HP condensing unit.
Is it normal to have a ball of ice built up on suction return on compressor?
Could there be evap fouling/superheat problems?
Cheers
-
12-10-2010, 09:33 AM #2
Re: ice build up on suction return?
You sure it's not short of gas?
-
12-10-2010, 10:11 AM #3
Re: ice build up on suction return?
to much liquid flooding back to comp?possible metering device issue?
-
12-10-2010, 10:18 AM #4
Re: ice build up on suction return?
Perfectly OK, just cool gas comimg back freezing the bell housing!
it is not at the crankcase!
-
12-10-2010, 10:28 AM #5
Re: ice build up on suction return?
What kind of suction line temp would you expect in this application?
Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
12-10-2010, 10:30 AM #6
Re: ice build up on suction return?
looks ok to me. Returning vapour could be as low as minus fifty so you are going to get some ice on the un lagged valve.
-
12-10-2010, 09:36 PM #7
Re: ice build up on suction return?
A few tempretures would help like sump & discharge .
Foaming of oil as well .
You don't see this so much on ***** applications but ammonia its quite common to have a good ice build up with -10 C application .
-
13-10-2010, 01:06 AM #8
Re: ice build up on suction return?
id be more concerned about the anaconda and from what i can see lack of mounting leg on the head fan.good luck getting your gauges on in a hurry.
have a tendency to agree with others about return vapour temperatures,time to check your superheats.mmm to beer or not to beer...........lets drink breakfast
-
13-10-2010, 04:20 AM #9
Re: ice build up on suction return?
You said its a blast freezer.
Typically, blast freezers are not on line 24/7 and are usually oversized in comparrison to a typical freezer. Make sure customer is using it as it was intended.
Quick Response:
> It can be normal: check your superheat at the compressor, at beginning of freeze cycles, and at the end. Customers sometimes try and use blast freezers as holding freezers as well. This can be a problem if the TXVs where over sized by design, or system wasnt designed for dual operation. For (Example: Your 45hp condensing unit was selected to meet the blast freezing conditions, however as a holding freezer only, it may only require a 5,10 or 15 ton system. Your TXVs in that senerio may not be able to throttle back. )
In either case, its always good to make sure you have an accumulator, oil seperator and in some cases a CPR or pressure limitting TXVs on any low temp units of that capacity.
-
13-10-2010, 04:43 AM #10
Re: ice build up on suction return?
As Frostyguy stated, as long as you have superheat you're ok. The ice formation simply means it's below dewpoint temperatures.
Thousands of HVACR manufacturers links! Visit: www.hvacrinfo.com
-
13-10-2010, 08:03 AM #11
Re: ice build up on suction return?
cheers for the ideas guys, I go back to site next week to check this freezer havent had gauges on to check superheat yet.
The site was badly looked after before I took over this week, all other chillers and freezers had badly fouled evaps and condensers.
Similar Threads
-
Copeland select 6
By Copman in forum Tools and CalculatorsReplies: 9Last Post: 27-05-2010, 09:01 PM -
Location of Suction Filter
By Ray123 in forum FundamentalsReplies: 2Last Post: 11-06-2009, 03:29 PM -
liquid return through suction line after hot gas defrost period
By coldkeeper1 in forum Supermarket RefrigerationReplies: 2Last Post: 19-06-2008, 10:07 PM -
Dry suction of one vessel into the wet of another!
By I LUV NH3 in forum NH3Replies: 0Last Post: 14-05-2008, 05:05 PM -
Benji
By benji in forum Trouble ShootingReplies: 29Last Post: 30-01-2008, 01:25 PM