    ice build up on suction return?



    Hi there,
    I have just taken over a maintenance contact of a blast freezer 45HP condensing unit.
    Is it normal to have a ball of ice built up on suction return on compressor?
    Could there be evap fouling/superheat problems?
    Cheers
    Attached Images Attached Images



  2. #2
    Join Date
    Feb 2010
    Location
    Ireland
    Age
    38
    Posts
    82
    Rep Power
    15

    Re: ice build up on suction return?

    You sure it's not short of gas?

  3. #3
    Join Date
    Jan 2010
    Location
    australia
    Age
    39
    Posts
    32
    Rep Power
    0

    Re: ice build up on suction return?

    to much liquid flooding back to comp?possible metering device issue?

  4. #4
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: ice build up on suction return?

    Perfectly OK, just cool gas comimg back freezing the bell housing!
    it is not at the crankcase!

  5. #5
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: ice build up on suction return?

    What kind of suction line temp would you expect in this application?
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  6. #6
    Join Date
    May 2005
    Location
    newbury
    Age
    44
    Posts
    13
    Rep Power
    0

    Re: ice build up on suction return?

    looks ok to me. Returning vapour could be as low as minus fifty so you are going to get some ice on the un lagged valve.

  7. #7
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,364
    Rep Power
    39

    Re: ice build up on suction return?

    A few tempretures would help like sump & discharge .

    Foaming of oil as well .

    You don't see this so much on ***** applications but ammonia its quite common to have a good ice build up with -10 C application .

  8. #8
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: ice build up on suction return?

    id be more concerned about the anaconda and from what i can see lack of mounting leg on the head fan.good luck getting your gauges on in a hurry.
    have a tendency to agree with others about return vapour temperatures,time to check your superheats.
    mmm to beer or not to beer...........lets drink breakfast

  9. #9
    Join Date
    Jun 2009
    Location
    United States
    Age
    59
    Posts
    10
    Rep Power
    0

    Talking Re: ice build up on suction return?

    You said its a blast freezer.
    Typically, blast freezers are not on line 24/7 and are usually oversized in comparrison to a typical freezer. Make sure customer is using it as it was intended.
    Quick Response:
    > It can be normal: check your superheat at the compressor, at beginning of freeze cycles, and at the end. Customers sometimes try and use blast freezers as holding freezers as well. This can be a problem if the TXVs where over sized by design, or system wasnt designed for dual operation. For (Example: Your 45hp condensing unit was selected to meet the blast freezing conditions, however as a holding freezer only, it may only require a 5,10 or 15 ton system. Your TXVs in that senerio may not be able to throttle back. )

    In either case, its always good to make sure you have an accumulator, oil seperator and in some cases a CPR or pressure limitting TXVs on any low temp units of that capacity.

  10. #10
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: ice build up on suction return?

    As Frostyguy stated, as long as you have superheat you're ok. The ice formation simply means it's below dewpoint temperatures.
    Thousands of HVACR manufacturers links! Visit: www.hvacrinfo.com

  11. #11
    Join Date
    Sep 2008
    Location
    New Zealand
    Age
    49
    Posts
    8
    Rep Power
    0

    Re: ice build up on suction return?

    cheers for the ideas guys, I go back to site next week to check this freezer havent had gauges on to check superheat yet.
    The site was badly looked after before I took over this week, all other chillers and freezers had badly fouled evaps and condensers.

Similar Threads

  1. Copeland select 6
    By Copman in forum Tools and Calculators
    Replies: 9
    Last Post: 27-05-2010, 09:01 PM
  2. Location of Suction Filter
    By Ray123 in forum Fundamentals
    Replies: 2
    Last Post: 11-06-2009, 03:29 PM
  3. liquid return through suction line after hot gas defrost period
    By coldkeeper1 in forum Supermarket Refrigeration
    Replies: 2
    Last Post: 19-06-2008, 10:07 PM
  4. Replies: 0
    Last Post: 14-05-2008, 05:05 PM
  5. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 01:25 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •