    Failed temperture sensor in Copeland



    A Industrial guy needs a little help.

    We have a older 30 HP, 3 phase, 480V Copeland at work. It operates a falling film chiller. Unfortunately I left the exact model number at work.
    This morning when I arrived my number one was trying to find why it did not start.
    The overheat protection control was open, preventing the machine from starting. The 3 sensors located on the motor were all showing open from common to the sensor leads. And then we got a reading of 1250 Ohms or so on each one. Scratching our heads we started the machine and it ran a few hours. Then the compressors stopped and we found the sensor leads open again.
    It did not take long to determine that the common lead was opening in the compressor. A decision was made to bypass the switch for the moment.
    I talked to a local Copeland re-builder I know and he said we could bring the compressor in and he most likely be able to fix the problem. It would be a small problem to get it out of it's location, and I would like to avoid the downtime.
    I am well familiar with sizing and using overloads to protect a external motor, but thought a refrigerant cooled motor might have other requirements. A Phase Monitor could also be included. I do not wish to risk a burnout and the required cleanup. Hot gas flows continuously to the evaporator on this chiller so I would have a excellent chance to contaminate the system if a burnout would occur.
    Any thoughts?



  2. #2
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Failed temperture sensor in Copeland

    I would look at Phase protection at the compressor terminals (after contactor and overload), discharge overheat stat. Short timed oil protection pressure switch and oil level.

Similar Threads

  1. Copeland scroll not engaging
    By fridgey in forum Trouble Shooting
    Replies: 6
    Last Post: 02-04-2010, 11:12 PM
  2. Copeland Modulating Controls? affect low temp evap?
    By marinechiller in forum Technical Speculations
    Replies: 0
    Last Post: 12-02-2010, 04:11 PM
  3. copeland scroll durability
    By Third_techtrio in forum Technical Discussions
    Replies: 16
    Last Post: 23-01-2010, 04:47 AM
  4. Copeland semi 7.5hp rewind etc
    By George Askew in forum Electrical
    Replies: 4
    Last Post: 26-11-2008, 07:58 AM
  5. copeland Digital Scroll
    By supermarketguy in forum Supermarket Refrigeration
    Replies: 3
    Last Post: 17-10-2008, 09:09 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •