R407C vs R22
If I were to change to R407C from R22
Would the head pressure be higher for R407 then R22
Would I have to adjust the HP control and the condenser fan cut in switch?
Is a HP condenser cut in at around 200 psig be adequate
-
10-04-2002, 01:11 AM #2Would the head pressure be higher for R407 then R22
Would I have to adjust the HP control and the condenser fan cut in switch?Prof Sporlan
-
10-04-2002, 09:08 PM #3
When you say changing to R407 from R22 do you mean as a "drop in"?
This is not possible without an oil change as 407 requires a synthetic oil. If you are talking about an a/c application then yes the compression is normally higher than that of 22 but we have not yet encountered discharge pressures anything like the levels referred to in the press or by word of mouth.
At evaporating temperatures around 5 deg C you can expect a drop in performance of about 5% but as the evaporating temperature drops to sub zero the performance duty drops off rapidly making this refrigerant unsuitable for low temperature applications.
-
14-04-2002, 05:35 PM #4
I have also heard that, in comparison to R22, R407C is more likely to condense out in the wet suction return line, and trash the compressor valve plates.
We were alerted to this when a compressor manufacturer refused to supply the contractor installing a 400kw A\C plant with the compressors the contractor originally wanted to use, based on the long suction pipe runs.
Has anyone actually had any experience of this where R22 has been changed to R407C on a big plant?
Steve
-
05-10-2010, 08:34 AM #5
Re: R407C vs R22
R22 gas low pressoure is grater then R407C, and high pressore is hier then R 22 gas. please tell me how much difrance between low & high presoures
Similar Threads
-
P/h chart for R407c
By Coolie in forum Technical SpeculationsReplies: 4Last Post: 29-05-2011, 06:17 PM -
R407C to R404a
By MaDiNfO in forum Air ConditioningReplies: 10Last Post: 30-07-2006, 09:34 AM -
R22 vs R407C.....................again!!
By Abe in forum Air ConditioningReplies: 5Last Post: 24-07-2003, 12:21 AM -
R407C composition
By Jai in forum Air ConditioningReplies: 4Last Post: 01-02-2002, 08:59 AM -
R407c
By Mike Hopkins in forum RefrigerantsReplies: 7Last Post: 14-12-2001, 05:29 PM