    UPS room A/C



    how suitable is a split A/C for an UPS room (±15 kW)?
    what is the recomended system?



  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    38

    Re: UPS room A/C

    Standard splits are OK as they usually have high SHR evaps. But you will need fresh air make up [ fan forced ] to keep humidity % up and consider humidity controller as well.

  3. #3
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: UPS room A/C

    Also consider extraction (possibly passive) at the heat source but keep the space on a positive pressure. This will reduce the load on cooling.

  4. #4
    Join Date
    Jun 2010
    Location
    Ireland
    Posts
    168
    Rep Power
    15

    Re: UPS room A/C

    personally do not recommend 'split' or comfort air conditioning for comms or ups rooms. Energy in these applications are almost 100% sensible where splits can have a sensible to latent ratio of as little as 45%. Two problems with this: you spec a 15kW unit but only 6.75kW are available, even if you spec a 33kW unit you take huge volumes of moisture out of the air which can lead to higher risk of static discharge.

    Other major no no is cassettes (we love em here), sure they don't take up any space but when (not if) the drain leaks your kit is right in the firing line.

    A number of close control specialist companies have very good plant with 'free' cooling

  5. #5
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: UPS room A/C

    I don't think a split system is suitable. And I don't think fresh air is a good idea.
    Close control units (possibly with free cooling) are the only suitable equipment for properly control high value assets.
    Also the average life time for a split system is calculated on few hundreds hours / year. An UPS system works 24/7/365.

    In my playfield, for a 15kVA good quality UPS, the heat load is approx 3 to 4kW.

  6. #6
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    38

    Re: UPS room A/C

    NNN, how does +/- 15 kw change to 15Kva.

  7. #7
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: UPS room A/C

    It doesn't. That was a bail for the poster, because UPS'es are denominated in kVA, not in kW.

  8. #8
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: UPS room A/C

    I have done one large servers room with large splits.

    Just measured the currant draw for the room, add 50% for the future and installed all the units.

    each cabin with severs had a top pulling fan installed, instead of remotes, a wired unit is controlling the temp. the temp control unit is connected to cellular line for high temp alarm.

    it works fine for past 2 years.

  9. #9
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: UPS room A/C

    UPS rooms do not need to be kept very very cool so it would be possible to set the room high to 25- 28 deg c and in that case a split will function ok.

    Daikin have a data room setting which will further enable it to run fine or even better fit a 7 kw indoor on a 6kw outdoor unit to get a better ratio (no warranty but better cooling)

Similar Threads

  1. Heat transfer coefficient - Coolpack
    By Graham in forum Fundamentals
    Replies: 10
    Last Post: 28-05-2008, 01:08 AM
  2. Freezer Room Panels
    By Feeze in forum Technical Discussions
    Replies: 10
    Last Post: 22-04-2005, 05:58 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •