Results 1 to 5 of 5
Threaded View
-
14-01-2005, 10:23 AM #1
method to design air cooled condenser
Hi there
sometime back i asked u people to tell me the way 2 design air cooled condenser . reply was not encouraging let me tell u how we design it
below is data given in MBH/sq.ft multiply it with Heat rejection ratio factor and multiply by face area u select.
u will get the capacity of coil.
note...all these data are experimental and are valuable in many ways as we do all designing based on it
if data below isnot clear then see the attachment
TOTAL HEAT REJECTION MBH/FT²
Following data is based on
Entering air temperature= 95°F
Condensing temperature= 125°F
Copper tube 3/8” Aluminum fins with plane tubes
2 ROW CONDENSER COIL PERFORMANCES
AIR VELOCITY @ COIL FPM
FPI 300 400 500 600 700
12 5.0 5.54 6.21 6.84 7.5
14 5.6 6.0 6.82 7.49 8.09
16 6.5 6.8 7.42 8.15 8.50
3 ROW CONDENSER COIL PERFORMANCES
AIR VELOCITY @ COIL FPM
FPI 300 400 500 600 700
12 6.6 7.5 8.5 9.4 10.12
14 7.5 8.0 8.93 9.86 10.90
16 8.2 8.6 9.36 10.32 11.68
4 ROW CONDENSER COIL PERFORMANCES
AIR VELOCITY @ COIL FPM
FPI 300 400 500 600 700
12 7.5 8.52 9.95 11.12 12.16
14 8.0 9.4 10.54 11.9 12.90
16 8.5 9.10 11.13 12.67 13.64Last edited by abbasi; 14-01-2005 at 10:26 AM. Reason: data was not clear
Our nose is our personal air-conditioning system: it warms cold air, cools hot air and filters impurities
Similar Threads
-
Air Cooled Condenser Design
By Samarjit Sen in forum Technical DiscussionsReplies: 7Last Post: 23-06-2011, 12:54 PM -
How to adjust head on a water cooled condenser
By kengineering in forum Technical SpeculationsReplies: 5Last Post: 30-05-2007, 10:37 PM -
water cooled condenser shell type
By abbasi in forum New TechnologiesReplies: 0Last Post: 27-04-2005, 08:32 AM -
air cooled condenser design
By abbasi in forum FundamentalsReplies: 1Last Post: 26-03-2005, 08:33 PM -
Trane Air cooled condenser
By jan behnke in forum Trouble ShootingReplies: 24Last Post: 05-08-2004, 07:31 AM