    scroll gone bad ?



    If my readings on the gauges look like suction is about equal to the head, on a scroll what's the way to know if it's bypassing not pumping or reversing valve is stuck in the middle ? I have yet to come across a full proof way ? Anyway thanks in advance for the help.. ...



  2. #2
    Join Date
    Dec 2008
    Location
    UK
    Posts
    55
    Rep Power
    16

    Re: scroll gone bad ?

    Compare Running Amps recorded now against previous logs, if substantially lower then it would suggest that the scroll is not pumping.
    Also perhaps feel the Dischsrge pipe, if not much warmer than suction this may also give some indication. Good luck.

  3. #3
    Join Date
    Nov 2003
    Location
    NSW, Australia
    Age
    40
    Posts
    242
    Rep Power
    21

    Re: scroll gone bad ?

    If it's a new install/replacement compresser I'd say it could be pumping backwards (3phase type). Or not uncommon here, grid upgrades or repairs where linesman crosses over phases on re-connect, this is where phase fail relay in control circuit invaluable!
    "Old fridgies never die, they just run out of gas!"

  4. #4
    Join Date
    Feb 2009
    Location
    UK
    Posts
    14
    Rep Power
    0

    Re: scroll gone bad ?

    Firstly are your gauges OK?
    You can hear a scroll if it is running backwards, if you are not sure Copeland scrolls are OK for a short time if you try reversing phase rotation.

  5. #5
    Join Date
    Nov 2003
    Location
    NSW, Australia
    Age
    40
    Posts
    242
    Rep Power
    21

    Re: scroll gone bad ?

    Ok to hear if your outside and it's the only unit running. Little harder in plantroom where you can't hear anything then add the ear plugs hehe
    "Old fridgies never die, they just run out of gas!"

  6. #6
    refman2010's Avatar
    refman2010 Guest

    Re: scroll gone bad ?

    if it sounds like its not running correct, reverse any two of the phases (if 3ph) this is common on scrolls!

  7. #7
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: scroll gone bad ?

    Hi. It would seem like thiOs guy is off the grid all good replys but no response
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  8. #8
    Join Date
    May 2008
    Location
    .
    Posts
    33
    Rep Power
    0

    Re: scroll gone bad ?

    What would happen if the compressor runs for a period of time with the phases incorrect? Would it cause the compressor to burn windings?
    I came across one a few days ago where they had problems with 3 phase power to the house. I think the compressor only had 2 phases for a period of time. The compressor is causing the RCD to trip.

  9. #9
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: scroll gone bad ?

    Of course, if the compressor runs on 2 phases, it burns shortly after. Inspecting it will show one winding perfectly ok, and 2 remaining windings burnt and widely overheated..

Similar Threads

  1. Digital Scroll VRF Systems & Inverter Systems
    By weeliang82 in forum Air Conditioning
    Replies: 22
    Last Post: 16-11-2010, 04:07 PM
  2. Copeland Scroll Advanced Protection Problems
    By dwayne in forum Trouble Shooting
    Replies: 8
    Last Post: 24-09-2010, 06:54 AM
  3. Discrete Scroll Compressor Model
    By gmansparky in forum Fundamentals
    Replies: 9
    Last Post: 22-05-2010, 02:20 PM
  4. Scroll compressor for Freezing application
    By georgedvf in forum Technical Speculations
    Replies: 18
    Last Post: 08-04-2010, 07:24 PM
  5. Digital scroll
    By archibaldtuttle in forum Commercial
    Replies: 3
    Last Post: 06-01-2010, 05:27 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •