Thread: scroll gone bad ?
-
31-07-2010, 03:47 AM #1
scroll gone bad ?
If my readings on the gauges look like suction is about equal to the head, on a scroll what's the way to know if it's bypassing not pumping or reversing valve is stuck in the middle ? I have yet to come across a full proof way ? Anyway thanks in advance for the help.. ...
-
31-07-2010, 10:48 AM #2
Re: scroll gone bad ?
Compare Running Amps recorded now against previous logs, if substantially lower then it would suggest that the scroll is not pumping.
Also perhaps feel the Dischsrge pipe, if not much warmer than suction this may also give some indication. Good luck.
-
04-08-2010, 09:45 AM #3
Re: scroll gone bad ?
If it's a new install/replacement compresser I'd say it could be pumping backwards (3phase type). Or not uncommon here, grid upgrades or repairs where linesman crosses over phases on re-connect, this is where phase fail relay in control circuit invaluable!
"Old fridgies never die, they just run out of gas!"
-
13-08-2010, 11:00 PM #4
Re: scroll gone bad ?
Firstly are your gauges OK?
You can hear a scroll if it is running backwards, if you are not sure Copeland scrolls are OK for a short time if you try reversing phase rotation.
-
14-08-2010, 05:30 AM #5
Re: scroll gone bad ?
Ok to hear if your outside and it's the only unit running. Little harder in plantroom where you can't hear anything then add the ear plugs hehe
"Old fridgies never die, they just run out of gas!"
-
17-09-2010, 03:45 PM #6
Re: scroll gone bad ?
if it sounds like its not running correct, reverse any two of the phases (if 3ph) this is common on scrolls!
-
18-09-2010, 11:12 PM #7
Re: scroll gone bad ?
Hi. It would seem like thiOs guy is off the grid all good replys but no response
THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
-
23-09-2010, 08:59 AM #8
Re: scroll gone bad ?
What would happen if the compressor runs for a period of time with the phases incorrect? Would it cause the compressor to burn windings?
I came across one a few days ago where they had problems with 3 phase power to the house. I think the compressor only had 2 phases for a period of time. The compressor is causing the RCD to trip.
-
23-09-2010, 10:29 AM #9
Re: scroll gone bad ?
Of course, if the compressor runs on 2 phases, it burns shortly after. Inspecting it will show one winding perfectly ok, and 2 remaining windings burnt and widely overheated..
Similar Threads
-
Digital Scroll VRF Systems & Inverter Systems
By weeliang82 in forum Air ConditioningReplies: 22Last Post: 16-11-2010, 04:07 PM -
Copeland Scroll Advanced Protection Problems
By dwayne in forum Trouble ShootingReplies: 8Last Post: 24-09-2010, 06:54 AM -
Discrete Scroll Compressor Model
By gmansparky in forum FundamentalsReplies: 9Last Post: 22-05-2010, 02:20 PM -
Scroll compressor for Freezing application
By georgedvf in forum Technical SpeculationsReplies: 18Last Post: 08-04-2010, 07:24 PM -
Digital scroll
By archibaldtuttle in forum CommercialReplies: 3Last Post: 06-01-2010, 05:27 PM