Results 1 to 12 of 12
Thread: Carrier 19XR CHILLER
18-05-2010, 08:28 AM #1
Hi, I have this problem on 600 ton chillers which are losing oil or should I say where it goes. We are adding refrigerant oil 2 gallons in a week. Pls. help or give ideas to troubleshoot. Thank you very much.
18-05-2010, 03:19 PM #2
Re: Carrier 19XR CHILLER
Hi :
If u leave your condenser pump running when chiller is off oil might MIGRATE AND accumalate in evaportaor
check your approach temp when unit is running u will probably find it very high in the evaporator
good luckTHE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
16-07-2010, 01:07 PM #3
I have a 19xrv chiller PIC-2 FRAME-3 with a wide evap. approach, dropped the cooler heads divider gasket was intact and okay pulled the charge, by weight its okay according to the name plate.Examined the float,and it was tight so I replaced the entire float Re-assemled made sure float pin and bubbler line lined up correctly, checked bubbler line with nitrogen,and it was clean.recharged 610 lbs 134A same probleme. Pulled charge again,checked liquid line ball valve for wear there was problemes with earlier machines and a service bulletin ,it was okay. Sent a camera through the evap liquid spray header it appeared to be clean.
Does anyone have any Ideas?
Thank you!!!
16-07-2010, 01:16 PM #4
CW and CHW isolation valve close when machine is in the unocc mode pd and flow rates were within design
16-07-2010, 04:45 PM #5
doos:
what is your email address I send you newsletter service
16-07-2010, 05:01 PM #6
scheylerproperties@hotmail.com or alex.chiller@ef.com
Thank you
22-09-2010, 04:24 AM #7
Newbie here............
I'm having very similar increased approach problems on 3 different machines (1)19xr 3 comp & 4 size hx and (2)xrv size3 comp & size five hx.
Evap approach stays consistent around 4 deg. design on the XR is 1.8 deg and the XRV's around 6.deg
*Flow is w/ in design
*added refrigerant then recovered it back. Due to discharge temp
*check divider gasket - good
I feel the float assembly inspection next?
Anyhow any feedback would be much obliged
Robert
22-09-2010, 04:26 AM #8
whoops typo thats .6 deg approach on the XRV's
22-09-2010, 11:25 AM #9
[quote=chiller15;203843]Newbie here............
Robert[/qu
22-09-2010, 11:42 AM #10
[QUOTE=TurboChiller;203875]Robert, here it is in a nut shell what I found is that the oil that was manufactured by others was not correct,it was a mix of mineral oil with poe this caused the wide approach,in the evaporator,and stopped the heat trasfer in the evaporator. These machines have enhanced tubes and the mineral gets in the grooves of the tubes,and retards the transfer of heat.What I would reccommend is taking both a oil sample and a refrigerant liquid sample from the evaporator (not vapor)and send it to a qualified testing lab(United Refrigeration). It could be a float but before I pulled the charge and disassemble the float I would check the refrigerant and oil that is a lot easier then pulling the float assembly. If you find that you have mineral oil in the refrigerant,I would be glad to give you my procedure on how to clean up the evaporator.
Robert if you find you have this probleme would you please let me know.
alex.chiller@ef.com
chillertechnology@gmail.com
22-09-2010, 01:52 PM #11
Hi im a newbie on here & currently struggling to find out how to post a new thread.....sounds stupid i know!
But im looking for a maintenance manual for the carrier container unit NT42-334-10. Can anyone help?
Thanks.
22-09-2010, 07:59 PM #12
Carrier Chiller Moisture Problem
By damo567 in forum CommercialReplies: 7Last Post: 22-01-2011, 08:58 AM -
Carrier chiller basic board problem
By noushad123 in forum Trouble ShootingReplies: 25Last Post: 17-06-2010, 06:55 AM -
Carrier Chiller Help
By superswill in forum Trouble ShootingReplies: 7Last Post: 18-01-2007, 10:06 PM -
Carrier chiller oil migration
By lowtech in forum IndustrialReplies: 5Last Post: 30-04-2006, 04:11 PM