    Hi,
    I have rebuilt an old air conditioner with the external board not working. I have replaced the capillary tube by two txv at evaporator and condenser (this is an heat pump).

    The inside unit is working fine, sends the signals to the reversing valve and compressor, thermostat, etc. so i just used some relays to feed the outside unit directly.

    The outside board should handle the defrost, that mostly happens with the capillary tube, but since now there is a TXV is there any concern about frost on the "evaporator" (outside)??

    Thanks



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: question regarding outside unit defrost

    Short answer - Yes.

    Frost builds to ice which blocks coil airflow and crushes pipes.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    May 2007
    Location
    Scotland
    Posts
    327
    Rep Power
    18

    Re: question regarding outside unit defrost

    The frosting up will occur according to ambient conditions and your evaporating pressure, not what expansion device you use.

    If the outdoor board controlled the defrost and is fed by your relays on the indoor unit then I can see why this is causing you a problem.

    I'd be interested to see a wiring diagram for the original control circuit and for your mods but wiring the lot from one panel inside sounds like the way to go...

  4. #4
    Join Date
    Jun 2009
    Location
    Arrentela
    Age
    36
    Posts
    32
    Rep Power
    0

    Re: question regarding outside unit defrost

    Quote Originally Posted by Contactor View Post
    The frosting up will occur according to ambient conditions and your evaporating pressure, not what expansion device you use.

    If the outdoor board controlled the defrost and is fed by your relays on the indoor unit then I can see why this is causing you a problem.

    I'd be interested to see a wiring diagram for the original control circuit and for your mods but wiring the lot from one panel inside sounds like the way to go...
    I haven't tried the unit yet, because the evaporator on the inside unit has an external equalized valve that doesn't have the one way valve to allow reversal of the refrigerant. The outside one has, although it is an internally equalized, so the unit is working only on cooling mode.

    The AC has two boards one on the inside unit, with the thermostat an one in the outside unit that reeded the outside temperature and witch one i think did the defrost, so I'm unsure if the internal unit handles the defrost (If yes, what was the function of the outside board!?)
    The inside one gives me the signals for the solenoid and compressor directly so i just wired two 24V relays to control them.

    I have seen on the web some posts about older units using a defrost timer that worked once 30 minutes or so, I thought i maybe using one. The temperatures in Portugal rarely go below 5ēCelcium.

    Thanks, Carlos

Similar Threads

  1. mitsibishi unit adresses
    By hard at work in forum Trouble Shooting
    Replies: 2
    Last Post: 23-06-2010, 06:54 PM
  2. LG Air Con Unit stuck on defrost
    By gio_ayr in forum Air Conditioning
    Replies: 8
    Last Post: 18-04-2010, 12:26 PM
  3. Change over 2 outdoor unit
    By bach in forum Air Conditioning
    Replies: 8
    Last Post: 08-06-2008, 06:55 PM
  4. mid-size refrigerated truck Thermo King unit question
    By coldkeeper1 in forum Transport
    Replies: 11
    Last Post: 11-05-2008, 09:42 PM
  5. Off-line Mitsi VRF leaks!
    By sinewave in forum Air Conditioning
    Replies: 8
    Last Post: 05-06-2007, 11:18 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •