    Rtac 200



    Hello guys,


    Small question, I have a RTAC 200 chiller which always cuts out in High pressure on one circuit.

    Thing is, the unit fails in HP even when it's not running. Trane here isn't very helpfull into comfirming it's the HP probe on the oil separator in the discharge line. Or an alternate pressure switch.

    The probe itself is an AKS from Danfoss. Has anyone of you ever had a problem with those probes ?

    Just in case anyone wonders, yes the condersors are clean, subcool etc is ok and the fans are all running in the right direction
    Last edited by wingman; 25-08-2010 at 07:14 PM. Reason: vocabulary ....



  2. #2
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: Rtac 200

    Quote Originally Posted by wingman View Post
    Hello guys,


    Small question, I have a RTAC 200 chiller which always cuts out in High pressure on one circuit.

    Thing is, the unit fails in HP even when it's not running. Trane here isn't very helpfull into comfirming it's the HP probe on the oil separator in the discharge line. Or an alternate pressure switch.

    The probe itself is an AKS from Danfoss. Has anyone of you ever had a problem with those probes ?

    Just in case anyone wonders, yes the condersors are clean, subcool etc is ok and the fans are all running in the right direction
    Link out the pressure switch if it still happens it's the probe if not it's the switch

  3. #3
    Join Date
    Dec 2008
    Location
    UK
    Posts
    55
    Rep Power
    16

    Re: Rtac 200

    Hi, Check out 2 stage HP switch behind HP Guage Plate. ( Danfoss/ Alco ) It may be that the second stage has tripped and needs reseting. You may need to remove the cover to access the second stage trip. Good luck.

  4. #4
    Join Date
    Aug 2008
    Location
    Belgium
    Age
    44
    Posts
    74
    Rep Power
    16

    Re: Rtac 200

    I'll check that one out moday, they have two of those machines for redundancy so . Plus it isn't that warm here anymore.

Similar Threads

  1. trane rtac 250 oil filter replacment
    By anish in forum Trouble Shooting
    Replies: 13
    Last Post: 29-01-2011, 02:14 PM
  2. trane RTAC alarm
    By HARRY 7 in forum Commercial
    Replies: 11
    Last Post: 21-10-2010, 06:00 AM
  3. Trane rtac 170
    By El Padre in forum Air Conditioning
    Replies: 5
    Last Post: 07-07-2009, 07:51 PM
  4. trane rtac 275
    By anish in forum Air Conditioning
    Replies: 6
    Last Post: 01-10-2008, 10:24 PM
  5. Trane RTAC Software Download
    By sean in forum Commercial
    Replies: 4
    Last Post: 30-09-2008, 12:36 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •