09-08-2010, 01:50 PM #1
New scroll shuts off after one minute!! Restart after 2??
Just installed a new 5 ton single phase Carlyle scroll compressor. started up and rans OK for 30 seconds. then shuts down for two minuts??? restarts then shuts down. changed all the stat componets. started with and with out potental relay.
230V single phase 19.5 amps, low sided 60 psi high 200 psi.
Old compressor was working fine. just had a stress crack in the compressor body (4 years old).
-
09-08-2010, 06:57 PM #2
Re: New scroll shuts off after one minute!! Restart after 2??
And your question is???
-
09-08-2010, 10:19 PM #3
Re: New scroll shuts off after one minute!! Restart after 2??
Maybe the problem is thermal overload tripping by the internal protection?
Maybe is working in a hard regimen which the motor is not prepared for.
What's the nominal and operational current? 19,5 Amps is nominal or absorbed? What's the other?To make progress is never good enough, I want to do better and better and better
-
10-08-2010, 05:15 PM #4
Re: New scroll shuts off after one minute!! Restart after 2??
Request from the vendor the correct starting equipment (and wiring schematics) for his compressor.
-
12-08-2010, 09:12 AM #5
Re: New scroll shuts off after one minute!! Restart after 2??
You need to carry out basic diagnostics and see what is stopping the compressor, has to be something on the control circuit telling it to stop, i'm sure the answer is right in front of you.
-
13-08-2010, 10:18 PM #6
Re: New scroll shuts off after one minute!! Restart after 2??
Discharge klixon?
-
14-08-2010, 08:50 AM #7
Re: New scroll shuts off after one minute!! Restart after 2??
check compr LRA amps check compr amps
-
14-08-2010, 03:38 PM #8
Re: New scroll shuts off after one minute!! Restart after 2??
...or it's passing a small current by some of windings directly to earth. Does the differential switch is tripping?
To make progress is never good enough, I want to do better and better and better
-
14-08-2010, 04:22 PM #9
Re: New scroll shuts off after one minute!! Restart after 2??
Hi Cygani.
Welcome to the forum.
Does this compressor have a control unit.
Or what make condensing unit is it fitted to?
It's just I cannot fathom what size system this comp would be attached to.
Therefore whether start delay and anti recycle timers are relevant?
More info is needed.
If it is indeed purely stand alone then the guys above have the logical answer covered.
Cheers Grizzly
Similar Threads
-
Digital Scroll VRF Systems & Inverter Systems
By weeliang82 in forum Air ConditioningReplies: 22Last Post: 16-11-2010, 04:07 PM -
Scroll compressor for Freezing application
By georgedvf in forum Technical SpeculationsReplies: 18Last Post: 08-04-2010, 07:24 PM -
Digital scroll
By archibaldtuttle in forum CommercialReplies: 3Last Post: 06-01-2010, 05:27 PM -
copeland ZR scroll vs VR scroll
By Lc_shi in forum Technical SpeculationsReplies: 7Last Post: 03-09-2008, 04:27 PM -
Dual Scroll Compressor
By ernestlin in forum Technical DiscussionsReplies: 7Last Post: 27-06-2006, 04:14 AM