    4 Drawer Cooler Problem



    Some guys I'm working with have been having a lot of trouble with a 4 drawer reach in cooler. It is a single unit, but has two evaps and txvs. I believe it had been freezing up on both evaps and had low low side pressure and high high side pressure.

    They replaced both txvs but still had the same problem. All it did was make the high side pressure higher and the low side lower. They tried adjusting them, but it didn't change the superheat or anything. They then suspected that when they put in the txvs, they overheated the powerheads (there wasn't enough room to remove them.) The unit was still icing up just back to the txvs.

    They replaced the powerheads on both, but that didn't help anything either. They are completely stumped now.

    Also, even though the high side pressure is about 300psi, the sightglass just shows a small amount going through, like a river. I'm not as experienced as they are, but it sounds to me like a kink in the line before or after the condenser, or some kind of plug there.

    Any ideas would be appreciated, thanks.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: 4 Drawer Cooler Problem

    High side of 300psi doesn't help when we don't know the refrigerant.

    Does sound like a blockage as you suspect, a good look around is needed. Perhaps use a contact thermometer across the various components to help find it.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    MikeGardner's Avatar
    MikeGardner Guest

    Re: 4 Drawer Cooler Problem

    Good idea on the thermometer, but half of the lines are behind a non removable table top. And I think its r404.

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: 4 Drawer Cooler Problem

    Quote Originally Posted by MikeGardner View Post
    Good idea on the thermometer, but half of the lines are behind a non removable table top. And I think its r404.
    Well of course they are, does any designer ever think about maintenance.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: 4 Drawer Cooler Problem

    Hi MikeGardner, just a thought, maybe the cooler is on the wrong refrigerant? Worked on a small coldroom marked R404a, 350psi pressure and poor cooling, changed it to R134a now runs fine.

  6. #6
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: 4 Drawer Cooler Problem

    blocked condenser pass or receiver inlet blockage has given me grief before.
    mmm to beer or not to beer...........lets drink breakfast

  7. #7
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,853
    Rep Power
    46

    Re: 4 Drawer Cooler Problem

    First thing i would check is the drier, don't know if it was changed at the same time as the txvs.
    Put a schreader valve in just before the txv and see if you have the same 300psi there, it should be pretty near to the same pressure.

  8. #8
    Join Date
    Sep 2007
    Location
    United States
    Posts
    167
    Rep Power
    17

    Re: 4 Drawer Cooler Problem

    Check model number on compressor and see what it ***** it was designed for. Who makes unit. If True or Continental chances are compressor is r134. Definitely take temps before and after drier. All else fails, a 4 drawer is relatively small capacity. Evacuate, blow out with nitrogen, change drier, pull a " good " vacuum and recharge to specs. Make sure condenser coil is clean and fan motor works. If problem returns, come on back with information and you'll find help !! Good luck.
    Don't leave it like you found it.....Leave it like it should be !!!

Similar Threads

  1. Samsung Vivace Problem AQV24VBCN
    By goldpau in forum Air Conditioning
    Replies: 0
    Last Post: 18-09-2009, 06:28 PM
  2. Trane CCUH oil problem
    By wingman in forum Air Conditioning
    Replies: 25
    Last Post: 04-08-2009, 07:07 AM
  3. Fabrication of Cooler Tube & Shell Cooler
    By rickyccong in forum Technical Discussions
    Replies: 1
    Last Post: 27-07-2009, 02:25 PM
  4. Furance problem
    By ALONEI in forum Trouble Shooting
    Replies: 10
    Last Post: 14-05-2008, 11:32 AM
  5. York Chiller Excessive Purges Problem
    By imranmd in forum Commercial
    Replies: 5
    Last Post: 07-03-2008, 05:13 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •