    tinnertech's Avatar
    tinnertech Guest
    changing line set
    Is it mandatory to replace the line set if your replacing the a coil and condensor and going from r22 to r410a? I've heard conflicting answers. Thanks for the help!
    3,853
    Re: changing line set
    If i was putting a system in for myself i would run a new line set, i would prefer to run a new line set on customers work too, but often they only look at the price.
    Is it mandatory? No, Is it advisable? Yes.
    Also depends on the quality of the existing pipework, is it suitable for the potential higher pressure?
    Apr 2010
    Delhi
    67
    Hi Brian_UK,
    for R22 head pressures are abt 300 psig max.
    how high is it for R410 gas.
    Kssoin
    Oct 2003
    5,630
    Kssoin, you can find this pressure in a log p/h chart of R410a, almost double.
    Will yu not change the compressors?
    If you perform after your job a pressure test on 1.1 x the max pressure your R410a system ever will see and it withstands this test pressure, well, then you can let your system run on the old pipework.