    Wrong pipes diameter - what now?



    Hello!

    My customer have new house with installations for multi split system. Installed pipes diameter are 1/2" and 3/8".

    I want install Mitsubishi sistem with outdoor unit MXZ-2A52VA and indoor units 2xMSZ-FD35VA.
    Pipes diameter for this system is 1/4" and 3/8".

    Can i reduce diameter on both sides of pipe with welding some pipe with right diameter?

    Pipes are approximate 25m long.

    Will system work? I calculate that i must add approximate 200g extra gas. Is this ok?

    Thank you!

    Igor



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: Wrong pipes diameter - what now?

    Can you push some 1/4" tube inside the 1/2", that way you will have the right sizes.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: Wrong pipes diameter - what now?

    Quote Originally Posted by Brian_UK View Post
    Can you push some 1/4" tube inside the 1/2", that way you will have the right sizes.
    I was thinking the same thing.

    25m (82 feet) is a long line set run. I would definitely check with Mitsubishi and get their recommendations for this length.
    Thousands of HVACR manufacturers links! Visit: www.hvacrinfo.com

  4. #4
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Wrong pipes diameter - what now?

    Quote Originally Posted by igi View Post
    Hello!

    My customer have new house with installations for multi split system. Installed pipes diameter are 1/2" and 3/8".

    I want install Mitsubishi sistem with outdoor unit MXZ-2A52VA and indoor units 2xMSZ-FD35VA.
    Pipes diameter for this system is 1/4" and 3/8".

    Can i reduce diameter on both sides of pipe with welding some pipe with right diameter?

    Pipes are approximate 25m long.

    Will system work? I calculate that i must add approximate 200g extra gas. Is this ok?

    Thank you!

    Igor
    What's the problem with pipes? Let see: You have 3/8" instead of 1/4" for liquid line » Good/BETTER (less pressure loss, less flash gas at TXV); you have 1/2" instead of 3/8" for suction line so less suction pressure loss. The only problem I see is the lack of oil return. However I think it should have no problem because I bet the vapor velocity will be still sufficient. If the condensing unit is below the evaporators levels no problem will have.
    To make progress is never good enough, I want to do better and better and better

  5. #5
    Join Date
    Dec 2008
    Location
    Slovenia
    Age
    45
    Posts
    11
    Rep Power
    0

    Re: Wrong pipes diameter - what now?

    Quote Originally Posted by Brian_UK View Post
    Can you push some 1/4" tube inside the 1/2", that way you will have the right sizes.
    No chance for this...

  6. #6
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: Wrong pipes diameter - what now?

    Quote Originally Posted by igi View Post
    No chance for this...

    Yes, good luck with that one brian feeding 25m of 1/4 up a 1/2 hole!

  7. #7
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Wrong pipes diameter - what now?

    Just let it work, With 25 m lengths, it will be fine.

    This Ac we are talking about, not science.

  8. #8
    Join Date
    Jul 2010
    Location
    Bulgaria
    Age
    46
    Posts
    17
    Rep Power
    0

    Re: Wrong pipes diameter - what now?

    no problem just add extra charge

  9. #9
    Join Date
    Jan 2007
    Location
    SPAIN
    Posts
    172
    Rep Power
    18

    Re: Wrong pipes diameter - what now?

    Main problem arises with the 3/8 replacing the 1/4 the valve/flow control is most likely in the outdoor unit (check this) this will lead to the refrigerant flashing/expanding too early before the evaporator. Compensating by more gas on these lengths would lead to more refrigerant in the system than that which it was designed for. Be aware of other consecuential effects when used as a heat pump.

  10. #10
    Join Date
    Dec 2008
    Location
    Slovenia
    Age
    45
    Posts
    11
    Rep Power
    0

    Re: Wrong pipes diameter - what now?

    Quote Originally Posted by momo View Post
    Main problem arises with the 3/8 replacing the 1/4 the valve/flow control is most likely in the outdoor unit (check this) this will lead to the refrigerant flashing/expanding too early before the evaporator.
    This is my greatest fear...



    [quote=momo;197699]Compensating by more gas on these lengths would lead to more refrigerant in the system than that which it was designed for. quote]

    I will add only 200-300g of refrigerant. This shoud not be a problem!


    [quote=momo;197699]Be aware of other consecuential effects when used as a heat pump. quote]

    ?


    Tomorrow i will see what will hapend...
    Thank you

  11. #11
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Wrong pipes diameter - what now?

    Quote Originally Posted by momo View Post
    Main problem arises with the 3/8 replacing the 1/4 the valve/flow control is most likely in the outdoor unit (check this) this will lead to the refrigerant flashing/expanding too early before the evaporator.
    I don't see how replacing 1/4 by 3/8 will the refrigerant flashing sooner...by the contrary.

    Igi, I believe no problem will happen.

    Give us feedback as soon you can.
    To make progress is never good enough, I want to do better and better and better

  12. #12
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Wrong pipes diameter - what now?

    Hi Igi,

    How is the AC working? Have it started up?
    To make progress is never good enough, I want to do better and better and better

  13. #13
    Join Date
    Dec 2008
    Location
    Slovenia
    Age
    45
    Posts
    11
    Rep Power
    0

    Re: Wrong pipes diameter - what now?

    Quote Originally Posted by Sandro Baptista View Post
    Hi Igi,

    How is the AC working? Have it started up?
    Yes I start it today...


    and its working like a charm for now...



    Thank you!

  14. #14
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Wrong pipes diameter - what now?

    Great to hear that.

    Keep in touch igi
    To make progress is never good enough, I want to do better and better and better

Similar Threads

  1. Fujitsu split pipes
    By gazza666 in forum Air Conditioning
    Replies: 10
    Last Post: 15-07-2010, 08:59 AM
  2. Only first half of Pipes freezing?
    By Bobbin in forum Commercial
    Replies: 6
    Last Post: 09-04-2010, 08:45 PM
  3. Alternative Pipe Diameter Calculation (?)
    By ice_cold in forum Fundamentals
    Replies: 7
    Last Post: 03-01-2010, 10:33 AM
  4. Running pipes in concrete
    By Jadeair in forum Supermarket Refrigeration
    Replies: 9
    Last Post: 10-11-2008, 09:24 AM
  5. Installing pipes
    By tuneee in forum Fundamentals
    Replies: 8
    Last Post: 05-06-2007, 08:21 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •