    I would like to ask you for advice. I’ve got the Lunite single phase compressor equipped with terminal box with the 63Amps contactor. I would like to know if that contactor is sufficient to do the job.
    This is the electric specification:
    Rated Current RLA: 20A
    Max Current: 30A
    Start Current: 100A
    That starting current makes me a bit anxious.
    Many Thanks,
    Sittard
    Sep 2003
    ISRAEL
    72
    4,248
    Re: Lunite FH4540Z
    No problem.
    Your 63amp contactor is sufficient to do the job.
    What you have to look at, is the MAX CURRANT.
    At start the contacts are closed and it takes less than a second for the compressor to run and drop the amps.
    When you disconnect the contactor at high currant, there is a big spark between the contacts and that is what kills contactors.
    scotland
    756
    Re: Lunite FH4540Z
    i have seen 10 hp 3 phase compressors on 32 amp contactors, your little pot will be fine!
    scotland
    756
    Re: Lunite FH4540Z
    http://www.actrol.com.au/PriceGuide/..._Section_4.pdf
    according to the above link fla are 7 amps
    3,853
    Re: Lunite FH4540Z
    Many contactors have the max motor hp/kw marked on them or on a chart on the box come in. I think your compressor is a 3hp model.
  1. l'unite hermetique
    By Andy AC in forum Commercial
    Last Post: 12-06-2009, 07:52 PM
  2. l'unite hermetique R12 Condensing unit
    By airefresco in forum Commercial
    Last Post: 08-02-2008, 09:08 PM
  3. Qualitair / L'unite compressor problem
    By wotsie in forum Trouble Shooting
    Last Post: 10-11-2007, 04:50 AM
  4. L'Unite hermetique wiring
    By Chilly willy in forum Electrical
    Last Post: 20-08-2007, 06:38 AM
  5. L'Unite Hermetique compressor
    By iceman007 in forum Commercial
    Last Post: 27-06-2004, 08:15 PM