Thread: RY71 daikin
-
26-07-2010, 01:43 PM #1
RY71 daikin
EO fault.' Quick start ' now smoking. Isolated ac. now what?
-
26-07-2010, 02:04 PM #2
Re: RY71 daikin
Probably get a new soft starter and capacitor if the outdoor PCB and compressor test OK.
Hyper engineering soft starters (quick start, sure start etc) are prone to fail, and those daikins use cheap chinese capacitors prone to fail.
-
27-07-2010, 01:26 PM #3
Re: RY71 daikin
Whats the full model number. FV1 / KV1 / KUV1
Chances are you are Talking about a F or early K series.
The safety circuit (2 orange wires) on the earier models were wired through the comp overload. Later was wired through the pressure switch.
If the comp doesn't start in a number of Sec the safety circuit activates. Problem was with it wired to the Comp overload is it only had one chance to start. The pressure switch gave it 6 chances. This eliminated nuisence safety activation due to poor power.
You can always remove the soft starter and run it without it.
Compressor could be stuffed. Meter it out.
Compressor could be seized. Disconnect softstarter and run direct online.
Quickstart could be stuffed. If above test works and comp runs then fit a surestart or run it without one.(Provided neighbors don't complain about lights dimming when comp starts)No longer Active
Similar Threads
-
Daikin not working... many problems
By stankovicv in forum Air ConditioningReplies: 26Last Post: 11-12-2010, 09:01 AM -
Daikin assistance or LACK of it!!
By brianocallaghan in forum Air ConditioningReplies: 7Last Post: 15-07-2010, 11:23 AM -
Mitsi City Multi VS Daikin VRV
By sumsor in forum FundamentalsReplies: 5Last Post: 14-07-2010, 05:54 PM -
Daikin AC parts from UK
By skel00 in forum Air ConditioningReplies: 5Last Post: 05-04-2009, 01:24 PM -
Fixing Daikin A3 Error
By Stuffy in forum Air ConditioningReplies: 3Last Post: 27-03-2009, 06:02 AM