    RY71 daikin



    EO fault.' Quick start ' now smoking. Isolated ac. now what?



  2. #2
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: RY71 daikin

    Probably get a new soft starter and capacitor if the outdoor PCB and compressor test OK.
    Hyper engineering soft starters (quick start, sure start etc) are prone to fail, and those daikins use cheap chinese capacitors prone to fail.

  3. #3
    Join Date
    Dec 2006
    Location
    Aust
    Posts
    68
    Rep Power
    18

    Re: RY71 daikin

    Whats the full model number. FV1 / KV1 / KUV1

    Chances are you are Talking about a F or early K series.
    The safety circuit (2 orange wires) on the earier models were wired through the comp overload. Later was wired through the pressure switch.

    If the comp doesn't start in a number of Sec the safety circuit activates. Problem was with it wired to the Comp overload is it only had one chance to start. The pressure switch gave it 6 chances. This eliminated nuisence safety activation due to poor power.

    You can always remove the soft starter and run it without it.

    Compressor could be stuffed. Meter it out.
    Compressor could be seized. Disconnect softstarter and run direct online.

    Quickstart could be stuffed. If above test works and comp runs then fit a surestart or run it without one.(Provided neighbors don't complain about lights dimming when comp starts)
    No longer Active

Similar Threads

  1. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 09:01 AM
  2. Daikin assistance or LACK of it!!
    By brianocallaghan in forum Air Conditioning
    Replies: 7
    Last Post: 15-07-2010, 11:23 AM
  3. Mitsi City Multi VS Daikin VRV
    By sumsor in forum Fundamentals
    Replies: 5
    Last Post: 14-07-2010, 05:54 PM
  4. Daikin AC parts from UK
    By skel00 in forum Air Conditioning
    Replies: 5
    Last Post: 05-04-2009, 01:24 PM
  5. Fixing Daikin A3 Error
    By Stuffy in forum Air Conditioning
    Replies: 3
    Last Post: 27-03-2009, 06:02 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •