Thread: Daikin VRV3 Commissioning
-
24-07-2010, 11:32 AM #1
Daikin VRV3 Commissioning
Hi guys
Can anyone tell me if you need to address the new Daikin VRV3 units on commissioning or do they set them selves up. As we have a unit with 11 units on it and when powered up the central control is not finding any units i would really like some help
Thanks
-
24-07-2010, 02:55 PM #2
Re: Daikin VRV3 Commissioning
You need to put in group numbers into each indoor unit. Once you do the first group number 88 will disappear.
You should start at group 1-00 for your first unit and then to 1-10 for your 11 indoor units.
Hold down test button for 4 seconds then timer up and down to set group numbers then press confirmation button once.(Depends on what controller you have)No longer Active