23-07-2010, 02:35 PM #1
Re: Solenoid Valves in Parallel Compressors Rack System
Yes, this is typical compressor pack / multiplex system. When the last of compressors stop, it is a common practice to stop it on a low pressure switch. This is referred as pump down procedure. At restart, when the SV opens, refrigerant fills up the vacuum created by the pump down, and the result is liquid hammering.
Register yourself and download the programmable controllers brochure form www.dixell.it . You can have a slight glance of the new ideas for the refrigeration sector
-
23-07-2010, 02:44 PM #2
Re: Solenoid Valves in Parallel Compressors Rack System
Ok, but when there's several rooms and only one room stops it's the same hammering and no compressor stops, so no pump down is happening there, right? I think the only solution for this is to install the SV near the TEV...
Register yourself and download the programmable controllers brochure form www.dixell.it . You can have a slight glance of the new ideas for the refrigeration sector
-
23-07-2010, 06:42 PM #3
Re: Solenoid Valves in Parallel Compressors Rack System
Just to get it right, so when using Parallel Compressors Rack and several rooms yo DO use SV neear as possible from the TEV to stop refrigeratn flow when set temperature is reached or defrost is required, right??
-
23-07-2010, 10:00 PM #4
-
23-07-2010, 06:01 PM #5
Re: Solenoid Valves in Parallel Compressors Rack System
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
23-07-2010, 09:59 PM #6
-
23-07-2010, 11:17 PM #7
Re: Solenoid Valves in Parallel Compressors Rack System
I totally disagree with this statement, the closer the better, if installed besides each other no hammer effect at all what DP you anyhow may see across the valve.
I had a judicial case about this with a loss of goods of over 250.000 € due to the long distance between SV and TEV.
We did measurements in both cases and DP can go to 100 bar.
It's also mentioned very clearly in the recommendations of Danfoss.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
Similar Threads
-
Daikin fault codes
By Chris2005 in forum Air ConditioningReplies: 45Last Post: 21-03-2012, 10:09 PM -
Pump down system, solenoid valve
By AleksanderNH in forum FundamentalsReplies: 6Last Post: 10-06-2010, 12:07 AM -
Parallel oil system problem
By Tom C in forum Technical DiscussionsReplies: 3Last Post: 04-06-2010, 12:19 AM -
Compressors - screw or reciprocating?
By Josip in forum Industrial CompressorsReplies: 18Last Post: 27-01-2009, 10:36 PM -
New Capacity Control Solution
By embrown in forum New TechnologiesReplies: 19Last Post: 30-12-2003, 01:33 PM