    Re: Solenoid Valves in Parallel Compressors Rack System

    Quote Originally Posted by georgedvf View Post
    NoNickName, I didn't understand the last part about prevent hammering stopping pump down. Since I'm talking about a Parallel Compressors Rack for several rooms.
    Yes, this is typical compressor pack / multiplex system. When the last of compressors stop, it is a common practice to stop it on a low pressure switch. This is referred as pump down procedure. At restart, when the SV opens, refrigerant fills up the vacuum created by the pump down, and the result is liquid hammering.

    Quote Originally Posted by georgedvf View Post
    Can you tell me more about what would be a "New age" control solution for this kind of systems? Where can I find info?
    Register yourself and download the programmable controllers brochure form www.dixell.it . You can have a slight glance of the new ideas for the refrigeration sector

  2. #2
    Join Date
    Oct 2007
    Location
    Mexico
    Age
    44
    Posts
    158
    Rep Power
    17

    Re: Solenoid Valves in Parallel Compressors Rack System

    Quote Originally Posted by NoNickName View Post
    Yes, this is typical compressor pack / multiplex system. When the last of compressors stop, it is a common practice to stop it on a low pressure switch. This is referred as pump down procedure. At restart, when the SV opens, refrigerant fills up the vacuum created by the pump down, and the result is liquid hammering.
    Ok, but when there's several rooms and only one room stops it's the same hammering and no compressor stops, so no pump down is happening there, right? I think the only solution for this is to install the SV near the TEV...



    Register yourself and download the programmable controllers brochure form www.dixell.it . You can have a slight glance of the new ideas for the refrigeration sector
    Thanks for that link, I will look into it.

  3. #3
    Join Date
    Oct 2007
    Location
    Mexico
    Age
    44
    Posts
    158
    Rep Power
    17

    Re: Solenoid Valves in Parallel Compressors Rack System

    Just to get it right, so when using Parallel Compressors Rack and several rooms yo DO use SV neear as possible from the TEV to stop refrigeratn flow when set temperature is reached or defrost is required, right??

  4. #4
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Solenoid Valves in Parallel Compressors Rack System

    Quote Originally Posted by georgedvf View Post
    Just to get it right, so when using Parallel Compressors Rack and several rooms yo DO use SV neear as possible from the TEV to stop refrigeratn flow when set temperature is reached or defrost is required, right??
    That's the general idea. Your mileage may vary.

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Solenoid Valves in Parallel Compressors Rack System

    Quote Originally Posted by NoNickName View Post
    ...At restart, when the SV opens, refrigerant fills up the vacuum created by the pump down, and the result is liquid hammering.....
    Not if teh SV is mounted just in front of the TEV.
    Carrefour , Colruyt and Delhaize, big Belgium supermarkets describe in their manuals you have to install the SV's as close as possible to the TEV.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  6. #6
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Solenoid Valves in Parallel Compressors Rack System

    Quote Originally Posted by Peter_1 View Post
    Not if teh SV is mounted just in front of the TEV.
    It doesn't matter. It probably is worse when the SV is near the TEV. Same hammering in less volume.

  7. #7
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Solenoid Valves in Parallel Compressors Rack System

    Quote Originally Posted by NoNickName View Post
    It doesn't matter. It probably is worse when the SV is near the TEV. Same hammering in less volume.
    I totally disagree with this statement, the closer the better, if installed besides each other no hammer effect at all what DP you anyhow may see across the valve.
    I had a judicial case about this with a loss of goods of over 250.000 € due to the long distance between SV and TEV.
    We did measurements in both cases and DP can go to 100 bar.
    It's also mentioned very clearly in the recommendations of Danfoss.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 10:09 PM
  2. Pump down system, solenoid valve
    By AleksanderNH in forum Fundamentals
    Replies: 6
    Last Post: 10-06-2010, 12:07 AM
  3. Parallel oil system problem
    By Tom C in forum Technical Discussions
    Replies: 3
    Last Post: 04-06-2010, 12:19 AM
  4. Compressors - screw or reciprocating?
    By Josip in forum Industrial Compressors
    Replies: 18
    Last Post: 27-01-2009, 10:36 PM
  5. New Capacity Control Solution
    By embrown in forum New Technologies
    Replies: 19
    Last Post: 30-12-2003, 01:33 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •