    dT on High Efficiency Units



    Why is it that dT on higher efficiency units is lower? I am getting about 8C (14.4 F) on my unit (COP 2.8, when OS temp is 30C, inside temp is 24C, inside RH is approx 65%) and while it is cooling okay, the dehumidification is not really adequate.

    Why is it, and is there anything I can do to change it?



  2. #2
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: dT on High Efficiency Units

    Hi amey01,

    Please reformulate better your question.

    OS is outside of the room? 8șC is the saturated suction pressure on the compressor?

    Why did you asked "Why is it that dT on higher efficiency units is lower?"
    To make progress is never good enough, I want to do better and better and better

  3. #3
    amey01's Avatar
    amey01 Guest

    Re: dT on High Efficiency Units

    Quote Originally Posted by Sandro Baptista View Post
    Hi amey01,

    Please reformulate better your question.

    OS is outside of the room? 8șC is the saturated suction pressure on the compressor?

    Why did you asked "Why is it that dT on higher efficiency units is lower?"

    Sorry if my question was unclear.

    By OS, yes - I mean outside.

    8C is the difference between the inside return air (at around 25C) and the air discharged from the duct nearest the evaporator (ie. the air discharged is about 17C).

    That leaves an 8C (or 14F) dT.

    I've heard that you should expect less on lower efficiency units?

  4. #4
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: dT on High Efficiency Units

    Quote Originally Posted by amey01 View Post
    I've heard that you should expect less on lower efficiency units?
    That DT you mentioned it's not thermal difference between the evaporating temperature and the medium air temperature.

    Using the aircooler unit you have can you lower the air flow passing through the coils by maybe changing winding connections delta » star? If not try to damp a a little the airflow.

    If you lower the airflow the outlet air temperature will be lower and you can condensing more water vapour from the air and so reaching closer the relative humidity you want. However the refrigeration capacity will be lower...but if your unit have no problem on reaching the temperature setpoint try it...then send me the feedback.


    Regards
    To make progress is never good enough, I want to do better and better and better

Similar Threads

  1. How are the Daikin Altherma units?
    By LucMan in forum Air Conditioning
    Replies: 11
    Last Post: 15-07-2010, 11:08 PM
  2. Replies: 30
    Last Post: 25-04-2010, 12:40 PM
  3. Mitsi VRF problem - not all units heating suffeciently
    By r0ss in forum Air Conditioning
    Replies: 17
    Last Post: 13-01-2010, 10:30 PM
  4. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  5. Air Cooled Mono Block Units & high Ambient
    By smpsmp45 in forum Technical Discussions
    Replies: 4
    Last Post: 11-12-2007, 06:29 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •