    Daikin not working



    I am not sure if Im posting in the right place but my daikin inverter with outside unit model = RXS71BVMA and indoor unit model number FTXS71BVMA was full of ice and I mean hard ice from recent bad weather in Australia. The only way to get rid of ice was to poor warm water over it. we left it for a day befoe turning back on and now the green light flashed and nothing was working. we turned it off at the power box and the light isnt flashing but its not doing anything at all, the outside unit isnt even starting up. I can put it in air con mode and it seems to work but still not the outside unit. When I checked the code on my remote it was U4 System Transmission between indoor units, and I dont know what that means?? Can anyone help, its soooo cold in Australia I want my heating back!



  2. #2
    Join Date
    Feb 2010
    Location
    Ireland
    Age
    38
    Posts
    82
    Rep Power
    15

    Re: Daikin not working

    Are u sure there are no breaks in the cable? Did u check the fuses in the outdoor unit?

  3. #3
    leah's Avatar
    leah Guest

    Re: Daikin not working

    please dont think im stupid lol BUT I dont know where to look on the outside unit for those things or even what im looking for?

  4. #4
    Join Date
    Dec 2006
    Location
    Aust
    Posts
    68
    Rep Power
    18

    Re: Daikin not working

    Leah

    Are you a tech or a customer.

    If you prove to me that you are a Tech then I will tell you what is wrong with your unit.

    If you are a customer then I would suggest that you get someone out that is a Tech because of the dangers associated. Even with the power off the outdoor unit can still have power on it due to the capacitors.

  5. #5
    leah's Avatar
    leah Guest

    Re: Daikin not working

    hi there no im not a tech thats why I didnt know where the fuses were, I did think I shouldnt be looking into any of it anyway just in case it voids my warranty which they said it could be covered. I have a tech guy coming and he said it sounds like I need a new pcb i think it was, thanks anyway just thought it might have been something simple guess not

  6. #6
    Join Date
    Dec 2006
    Location
    Aust
    Posts
    68
    Rep Power
    18

    Re: Daikin not working

    Most likely PCB or Fan motor. Fan motor can drain power from PCB if tight. This will cause u4 .
    Tech will be able to test this.

    Cheers
    No longer Active

  7. #7
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Daikin not working

    U4, how to check fan motor:...then you must check additionally the blinking LED under the cover (where wires are attached) of the outdoor unit and see if this LED blinks or if it's steady.
    You first have to check with fan and then a second time disconnecting the fan on the PCB (left undercorner on the PCB) after shutting Off main supply to the outdoor unit of course.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  8. #8
    Join Date
    Jul 2008
    Location
    london
    Posts
    102
    Rep Power
    16

    Re: Daikin not working

    Sorry Which unit was covered in Ice? Bad weather of ice buildup on pipes/coil?

  9. #9
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Daikin not working

    Correcting, testing this led of course while unit is connected to the mains.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  10. #10
    Join Date
    Dec 2006
    Location
    Aust
    Posts
    68
    Rep Power
    18

    Re: Daikin not working

    I would place money on fan motor seizing. This will drop airflow across outdoor coil and cause premature icing while indoor on heating.
    When motor failed completely draining power from outdoor PCB and causing U4.
    I would check for led's.
    If no led's turn power off / disconnect motor/ Turn power on and see if you have led's back. If yes then motor is problem.

    To test motor disconnect from PCB /Take fan blade off and spin shaft on motor with fingers(should get about 1 1/2 revolutions. If you dont and motor is notchy them this confirms motor is faulty. Must take off blade or there is too much leverage to tell. Also never disconnect motor or connect while power is on. If you dont zap yourself you will blow the PCB.
    No longer Active

  11. #11
    Join Date
    Mar 2010
    Location
    England
    Posts
    41
    Rep Power
    0

    Re: Daikin not working

    Spinning the motor by hand will not confirm failure, design of the motor means that it does not spin freely. Only way to confirm motor failure is by resistance test. Service manual explains test procedure.

  12. #12
    Join Date
    Jul 2008
    Location
    london
    Posts
    102
    Rep Power
    16

    Re: Daikin not working

    As above would try to check motor first then maybe board. Should say inside cover how check fault via outdoor pcb board led lights.

    Regards

  13. #13
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Daikin not working

    Quote Originally Posted by Crash Pilot View Post
    ...
    I would check for led's.
    If no led's turn power off / disconnect motor/ Turn power on and see if you have led's back. If yes then motor is problem.....
    I can be wrong but according to what I've seen in the field, its s blinking or steady LED, not led off.
    Correct me if I'm wrong, never too old to learn .
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  14. #14
    Join Date
    Dec 2006
    Location
    Aust
    Posts
    68
    Rep Power
    18

    Re: Daikin not working

    Spinning the motor by hand will not confirm failure, design of the motor means that it does not spin freely. Only way to confirm motor failure is by resistance test. Service manual explains test procedure


    Spinning the motor by hand will confirm the fault. Majority of motor failures on this model are due to failed rear bearing. When you spin the motor staff it will spin up to one and a half turns and feel slightly notchy. When the motor bearing is faulty the motor will be locked and very hard to turn.

    Agreeded that metering the motor out is important however with a u4 it is usually associated with a locked motor and not a electrical problem with the motor.
    This is based on what I have found however feedback from everyones experiences is what we need on this forum.
    No longer Active

  15. #15
    Join Date
    Mar 2010
    Location
    England
    Posts
    41
    Rep Power
    0

    Re: Daikin not working

    Was there not an issue with 4 way valve coil causing u4 errors on these types of units. I seem to remember this was a possibility
    Last edited by Mentallist; 15-07-2010 at 09:16 PM.

  16. #16
    ANDREASGR's Avatar
    ANDREASGR Guest

    Re: Daikin not working

    hi
    u4 contact problem with internal replacement outdoor unit and pcb control cable communication

Similar Threads

  1. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 09:01 AM
  2. Old Daikin Multi system, help please!
    By ArisL in forum Trouble Shooting
    Replies: 4
    Last Post: 19-07-2010, 07:10 PM
  3. Daikin FDYQ200PV1 - not so quiet
    By Mick301 in forum Air Conditioning
    Replies: 0
    Last Post: 27-11-2009, 11:11 AM
  4. Fixing Daikin A3 Error
    By Stuffy in forum Air Conditioning
    Replies: 3
    Last Post: 27-03-2009, 06:02 AM
  5. is my fridge working properly?
    By vincec in forum Trouble Shooting
    Replies: 1
    Last Post: 15-01-2002, 09:55 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •